Answer / ayaz
first communicate ccr tag conform and turn MOS if required
when 5 way manifold
1 hp side close
2 equalizer open
3 lp side close
and then hp and lp drain or vent should be open
the transmitter will show zero if not calibrate it
first adjust the zero
2nd second span check and adjust
and then service
1 drain or vent close
2 equalizer close
3 and then hp side open and lp side open
| Is This Answer Correct ? | 3 Yes | 0 No |
What is difference between scada and virtual instrumentation?
two common seiling liquid used in seal pots are:
What is cascade control in process instrumentation?
4 Answers Engineers India, ITC Infotech,
which instrument is used to study the structure of phloem and xylem tissue?
please send me the inteview questions in IOCL
How much voltage we get between two wire of 4 to 20 ma output? Is this voltage up or down respectvice to 4 - 20 ma ?
what is "smart" in smart transmitter ?
How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can u give me Answer.
What are the uses of orifice plates?
hi i am eswar i want to know the instrumentation interview questations for eil(engineers india ltd) i have applied for engineer post in eil please help in this.my mail id eswar310@gmail.com
How r the calculation of process line mpm.
0 Answers Bhushan Power Steel,
What is the potential contact / output??
1 Answers Vasava Engineering Private Limited,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)