Answer / ayaz
first communicate ccr tag conform and turn MOS if required
when 5 way manifold
1 hp side close
2 equalizer open
3 lp side close
and then hp and lp drain or vent should be open
the transmitter will show zero if not calibrate it
first adjust the zero
2nd second span check and adjust
and then service
1 drain or vent close
2 equalizer close
3 and then hp side open and lp side open
| Is This Answer Correct ? | 3 Yes | 0 No |
Profibus DP is a multi-master system. Would it work on RS-485 4W or not, and justify your answer
Why using negative voltage in vibration measurement?
Explain why plc require in analog input 4-20amp & 0-10 volt?
if in a level tx height is given, how u calculate the ranges of the tx?
2 Answers Bombay Rayon Fashions, Invensys,
how to calculate flow by dp transmitter?
We have yokogawa cs3000 one fcs and 4 his. After download to his, showing successfully at es, but not transferred to his.
how to adjust relay in smart positioner ?
WHAT IS SELF CLEAN ELCTRODE IN MAGNETIC FLOWMETER?? WHAT DO YOU MEAN BY THIS TERM??
what is instrument philosophy
purpose of absolute ppressure transmitter applcation?
EXPLAIN PROPOTIONAL INTEGRAL DERIVATIVE CONTROL ACTION?
why we are using analytical instrument in plant ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)