i want to calibrate a transmitter in the range of -100 to
300 mmwc. How it is possible to measure -100 to 300?.
Answers were Sorted based on User's Feedback
Answer / carl_ellis
Atmospherice pressure equals zero pressure (gauge).
Vacuum pressures are less than atmospheric so are negative with respect
to atmospheric pressure. -100mm would be a vacuum pressure.
Pressures above atmospheric are positive with respect to atmospheric
pressure.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / carl_ellis
-100mm wc is a vacuum with respect to atmospheric pressure
as a reference.
Given the range, the pressure transmitter is likely a
differential pressure transmitter.
-100mm wc pressure can be produced with a vacuum source,
like a hand pump connected to the high side, with the low
side open to atmosphere.
Or 100mm wc positive pressure can be applied to the low
side, with the high side open to atmosphere:
DP = high side minus low side
DP = 0 minus 100 = -100mm wc
The URV, 300mm wc, is a calibrated with a pressure source
connected to the high side, with the low side open to the
atmosphere.
Carl Ellis
Measure First
| Is This Answer Correct ? | 0 Yes | 0 No |
Will Intergraph support SmartPlant Instrumentation in an AutoCAD or MicroStation environment on a long-term basis?
What is Difference between Bench Set & Operating Range of Control Valve?
what is weighfeeder
If i have 4 Allen Bradely make RS logix 5000 PLC and for viewing that we are using 4 RS view SCADA for 4 different packages. Now, I will want to view two packages on only one SCADA. Then how i will do it?
What unit is used for measuring comp. outlet flow. it is CFM, M3/hr or NM3/hr. ?
How do you identify between actual alarm and false alarm in a Temperature Transmitter in SCADA based Control System
1)What is the suitable MOC for flow meters working at temperature between 200 - 250 cen. 2)In which application the mass flow meters are not advisable 3)Is it advisable to use radiation type or radar type instrument for non contact application
What is the difference between a Extension cable and a copnesating cable.Where can we use compensating cable. Is anywhere compensating cable are used for mv transmission to the indicator.
Which is the best field foundation bus. ( FF ) Yokogawa, Honeywell or others ?
what will be the pressure in tank which has the total level of 2 meters and is filled 1.2 meters ?
Isometric drawings are generated during _________________ phase of a project
what is differential pressure transmitter and transducer? how to work?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)