i have 2 motor of same rating. on no load condition one
motor take 1.6A but other motor is taking 4.8A. what is the
reason of this. please explain with proof.
Answers were Sorted based on User's Feedback
Answer / b.b. singh
one motor has connected in star then it taking 1.6A &
another is connected in delta so it taking 4.8A.
Is This Answer Correct ? | 16 Yes | 1 No |
In case of 3 phase motors,
the motor takes higher current might have incorrect winding ratio which may cause unbalancing of 3 phase current.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / ashok sharma
OK. It is right that in star motor taking 1.6A & in delta
motor is taking 4.8A. but Please prove this with example.
Suppose both motors are new .
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / sivakumar
FIST U WILL CHEK THE HP RATHIG THEN NEXT CHEKED AMPS
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / loboreliance2003
The motor drawing 1.6A on no load appears to be okay.The
motor drawing 4.8A on no load appears to have a fault. the
winding may be having not proper megger value. Or even
rewinding of this motor may have been done improperly. You
will not find this condition in new motors from original
manufacturer.
Is This Answer Correct ? | 2 Yes | 5 No |
Answer / sakthivel
first you are check the bearing and terminal board and all
so check starter conduct knob and verify the electrical
parameter and all check pump and so impellerside
Is This Answer Correct ? | 0 Yes | 3 No |
how many earthing should give for transformer body and nuetral
As a good company employee, can you report your supervisor to the company management if he or she is going against the company interest in his or her actions?
Whether power factor should be high or low? Why?
If we have 11 kv RYB Phase single core cable near about. Then wht effect and losses
Why transformer used in UPS??
how to calculate energy of 3-phase motor?
i have dry type transformers can you help me that how many tests i can do to know the performence of transformer and also please tell me about the BDV test and Insulation resistance test in oil cooled transformers
What will happen if i used 11KV earth ht kit to 11 KV / 11 KV cable termination?
Why star delta starter is preferred with induction motor?
working principle of induction motor is similar to transformer. but what makes it to rotate? then why the transformer doesnt?
what is the difference between ac and dc?
we done magnetic balance test for 33KV /440V transformer in our company , but the ratio out is confusing us Voltage applied in RY = 440 , at RB = 320 and YB = 60 RY 440 = ( RB + YB ) 380 only Please let me know what type of problem is it.