i have dry type transformers can you help me that how many
tests i can do to know the performence of transformer and
also please tell me about the BDV test and Insulation
resistance test in oil cooled transformers
Answers were Sorted based on User's Feedback
Answer / s ghosh thakur
The following tests to be done during commissioning.
1.Duster value.
2.PI test The value should be above2.o
3.Tan delta test.
4.Ratio test.
5.short ckt.impedance test.
6.vector test.
7.IR test.
8.Polarity test. Thats are sufficient.
BDV value of TRANS OIL should not be less than 50 kv.
IR value of oil cooled trans should be 100M w.r.t gr.and HT
to LT also 100M.PI test should carried out value min 1.5 to
2.0
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / brijesh soni
yes this ans is right you may be test Oppen circuit test,
Megnetic bellence test And very important Inples test.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nithiya
tan dalta test only for above 220KV higher rating
transformers only conducted , Impuls test only conduted in
factory only..and Asper IS 1866-2000 less then 72KV=40KV,
170KV=50KV above 170KV=60KV.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pinaki chatterjee
according to all routine test as per IS-2026 PART 1 and magnetic balance, also current balance test should be require if necessary temperature rise test can be made.
if the voltage level is 11 kv so IMPULSE TEST AS PER clause 12 can be made for better acivement.
partial discharge should always check
| Is This Answer Correct ? | 0 Yes | 0 No |
How to calculate the Airconditioner capacity for a standard telecom BTS shelter?
Why does the Solid state Rectifiers for 3-ph brake motors sometimes have 2 & sometimes 3 output terminals?
what is the load amp of a 2 hp single phase motor?
why voltage coil in wattmeter called as pressure coil why the pressure term is used in wattmeter?
Why Drives are used to run AC motors?
While testing LA mast,What are the parameter limits ?
what is resistance?
Is it really necessary to have reactive power in transmission line to transfer the power from one place to other?
if we convert kva into Ampers,which one formula use by us,pls tell me?
Has someone here done a sizing for a generator (3 phase), its for a pumping station. If you have an example for standby/duty and both running (I) star delta (ii) Soft Starter.
How to discharge the battery as quickly as possible ?
what is the maximum permissible limit value of leakage current and leakage counter reading to replace lightining arrester?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)