i have dry type transformers can you help me that how many
tests i can do to know the performence of transformer and
also please tell me about the BDV test and Insulation
resistance test in oil cooled transformers
Answers were Sorted based on User's Feedback
Answer / s ghosh thakur
The following tests to be done during commissioning.
1.Duster value.
2.PI test The value should be above2.o
3.Tan delta test.
4.Ratio test.
5.short ckt.impedance test.
6.vector test.
7.IR test.
8.Polarity test. Thats are sufficient.
BDV value of TRANS OIL should not be less than 50 kv.
IR value of oil cooled trans should be 100M w.r.t gr.and HT
to LT also 100M.PI test should carried out value min 1.5 to
2.0
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / brijesh soni
yes this ans is right you may be test Oppen circuit test,
Megnetic bellence test And very important Inples test.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nithiya
tan dalta test only for above 220KV higher rating
transformers only conducted , Impuls test only conduted in
factory only..and Asper IS 1866-2000 less then 72KV=40KV,
170KV=50KV above 170KV=60KV.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pinaki chatterjee
according to all routine test as per IS-2026 PART 1 and magnetic balance, also current balance test should be require if necessary temperature rise test can be made.
if the voltage level is 11 kv so IMPULSE TEST AS PER clause 12 can be made for better acivement.
partial discharge should always check
Is This Answer Correct ? | 0 Yes | 0 No |
What are the reasons for AVR failure in LT DGsets ?
What is a Servo Stabliser.
what is TRCC
Why inductor short on dc and capacitor allow to flow ac?
How does frequency affect KVA rating of a transformer? If a 500 kva, 500 to 250 v, 60 hz t/f used in Canada is to be operated on 50 hz in Europe frequency then how will its KVA rating change? a-increase b-decrease c-remains same
What is Difference Between Induction Motor & Servo Motor
31 Answers Jindal, Kirloskar, KTTM, Star Technocrates, Toyota,
wats the procedure to calculate no of batteries for ups?
hoe to test voltage restrained overcurrent relay?
what will happen at the time of CT saturation?and what will be the Relay's function at the time of CT saturation?
Can we use 1.1x 2 split air-conditioning at a same time in 2kw power loadar
what is polarity in ac system? and how do identified?
7. A resistance of 30 ohm is connected across 240v supply. If a resistance R ohm is connected in parallel with 30ohm resistor across the same supply, the current drawn becomes triple of original one The unknown resistor R is