i have dry type transformers can you help me that how many
tests i can do to know the performence of transformer and
also please tell me about the BDV test and Insulation
resistance test in oil cooled transformers
Answers were Sorted based on User's Feedback
Answer / s ghosh thakur
The following tests to be done during commissioning.
1.Duster value.
2.PI test The value should be above2.o
3.Tan delta test.
4.Ratio test.
5.short ckt.impedance test.
6.vector test.
7.IR test.
8.Polarity test. Thats are sufficient.
BDV value of TRANS OIL should not be less than 50 kv.
IR value of oil cooled trans should be 100M w.r.t gr.and HT
to LT also 100M.PI test should carried out value min 1.5 to
2.0
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / brijesh soni
yes this ans is right you may be test Oppen circuit test,
Megnetic bellence test And very important Inples test.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nithiya
tan dalta test only for above 220KV higher rating
transformers only conducted , Impuls test only conduted in
factory only..and Asper IS 1866-2000 less then 72KV=40KV,
170KV=50KV above 170KV=60KV.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pinaki chatterjee
according to all routine test as per IS-2026 PART 1 and magnetic balance, also current balance test should be require if necessary temperature rise test can be made.
if the voltage level is 11 kv so IMPULSE TEST AS PER clause 12 can be made for better acivement.
partial discharge should always check
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the formula for computing cable tray size & capacity
There is air in a room . the top and bottom of the room are at constant temp. T1 and T2. DRAW THE temp profiles if a. T1 greater than T2 b. T1 less than T2
Direction of flow of active power and reactive power with logic?
1 ton AC takes how much current( starting & stable)
what is the full form of MEMO? name of memo train.
we have 3*1 MW generator one NGR is common for all it will be selected during paralle our problem is two generator ca be paralled but when slecting third one we need to close NGR selection on third one other wise voltage not matching why?
what are the safety measure & controls in engine?
what is ISF
which motor have relatively high power factor and what is reason for have high pf? 1.capacitor run motor 2.shaded pole motor 3.capacitor start motor 4.split phase motor
150 hp moter how many kwh in 1 hour and what forfula 3 phase kwh.
5 Answers College School Exams Tests, CPCL, Syncom, Thermax,
What is the difference between bundled conductors and double circuit?
What will be the capcity of 3 phase DG set require for 25 KVA single phase lighting load?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)