how many earthing should give for transformer body and
nuetral
Answers were Sorted based on User's Feedback
Answer / bharat
According to IS standard 3043, 2nos of earth connections
shall be given from both the transformer body & transformer
neutral to individual earth pits.
Is This Answer Correct ? | 14 Yes | 1 No |
Answer / praveen shylesh
minimum 2 earthing for body and minimum 2 Earthing for
Nuetral
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / biswarup sarkar
hi i am biswarup of bata india.
earth electrode of 1 set transformer is 4
Is This Answer Correct ? | 0 Yes | 1 No |
What are Line losses and how can be it minimized/controlled.?
how to calculate load if i have three phase & single phase connection from power transformer( in term of kw & kva).can i take single phase load/3 for total kw calculation
Which cable is use for rtcc control panel
Simultaneous trip of incoming and outgoing breakers of 400kv/220kv trnasformer. What are the probable causes?
What is non-minimum phase transfer function?
PLEASE EXPLANE WHAT IS " MOSFET AC CONVERTER"? WHERE AND HOW IT IS USED?
Is there is any hazard to insulation of 3hp motor 5 KV megger is used for it?
What is the rate of WCT on the Electrical Contracts comprising of DG Sets and Civil Works in Delhi ?
0 Answers MES Military Engineer Services,
lead acid battery electrolity?
what is the difference between ac and dc?which one is more efficient?and what r their advantages
How can we find the breaking capacity of a Load breaker switch (LBS) fed from 11 kv supply??ex:50KA, 26kA etc???detailed step vice answer pls.
what is synchronous speed.? if an induction motor is made to run at full load, then is this synch. speed too..?