Why we use 4 - 20 ma?
Answers were Sorted based on User's Feedback
Answer / sam daniel, marthandam, kanyak
To operate a Digital signal we need 1-5Vdc. For Analog
Instruments we are using 250 ohms as load resistance. When
we converting this signal into current By Ohm's
Law V=IR
I=V/R
Put, V=1V Then I=1/250=4mA
Put, V=2V Then I=2/250=8mA
Put, V=3V Then I=3/250=12mA
Put, V=4V Then I=4/250=16mA
Put, V=5V Then I=5/250=20mA
*Also, since this is linear region
*Not possible to cause spark
*Since it is a current signal we can transmit it into long
distance.
*Suppose if the instrument is dead we can identify it.
Is This Answer Correct ? | 62 Yes | 3 No |
Answer / jayaraj
1}///in earlier days we had used BJT transister in signal
conditioning circuits for amplification purposes so in BJT
transfer characteristics 4 to 20 milli amps is a linear
region,....but now-a-days we re using cmos only.... as a
convention only we are following this 4-20 range
2}///another reason...for not using 0 milli amp
coz if we use like that we cannot distinguish between true
signal zero and dead zero(break in wires)
Is This Answer Correct ? | 46 Yes | 2 No |
Answer / nileshkumar
1) 4 - 2 ma signal can transmited long distance without
signal drop in cable.
2) To operate a Digital signal we need 1-5Vdc. For Analog
Instruments we are using 250 ohms as load resistance. When
we converting this signal into current By Ohm's
Law V=IR
I=V/R
Put, V=1V Then I=1/250=4mA
Put, V=2V Then I=2/250=8mA
Put, V=3V Then I=3/250=12mA
Put, V=4V Then I=4/250=16mA
Put, V=5V Then I=5/250=20mA
*when two connection short no sparking.
*Since it is a current signal we can transmit it into long
distance.
*Suppose if the instrument is dead we can identify it.
Is This Answer Correct ? | 5 Yes | 1 No |
in 4-20ma we can easily check the zero and wire breaking in
transmitter. Analog card accept 1-5v dc supply. thatsy V-IR
I=V/R
V=1V R=250OHMS
1/250 = 4MA
V=2V THEN I=2/250 = 8MA
V=3V THEN I=3/250 =12MA
V=4V THEN I= 4/250 =16MA
V=5V THEN I=5/250 = 20MA.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / anish kumaran r
Live zero and minimum current required to keep alive the tx
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / suresh nagdeo
another reason from starting current from 4 ma is between two cables maximum induced current is always below 4 ma. if electrical and instrumentation cables running together this type problems arised.
Is This Answer Correct ? | 0 Yes | 0 No |
WHAT IS A SYMPTOM OF FAULT WITH THE SPAN OF AN INSTRUMENT? 1)ZERO-POINT AND 100% ARE CORRECT BUT NOT A MID-RANGE. 2)ZERO-POINT IS CORRECT ,BUT 1005 INPUT IS NOT GIVING 100% OUTPUT. 3)LINEARITY PRBS. 4)1005 O/p IS CORRECT BUT ZEO POINT IS WRONG.
What is mean by trim?
How can SmartPlant Instrumentation users take advantage of these global services?
What is the Relation Between flow and pressure. How both terms related with each other.
where using the 0-20ma in feiled instrumentation? why its using?
Could you explain to me the enraf (servo gauge) mechanism. How it works ? and how it is working on archimedes theory while it's not immersed into the surface? and how can we calibrate it ? Thanx
please send data bank of quetions answers on analytical instrumentation.
defination of radial vibration?
What is the formula To convert Degree centigrade to foranhight.
what is IPS (instrument protective system)?
units of pressure,flow, level,temperature? principle of pressure gauge? calibration of pressure tx., level tx., temperature tx.flow tx.? description of two wire ,three wire and four wire R.T.D.? WHAT IS INPUT AND OUTPUT OF TX.? WHAT IS INPUT AND OUTPUT OF R.T.D. AND THERMOCOUPLE? WHAT IS HOT LOOP AND COLD LOOP? WHAT IS INPUT AND OUT PUT AND OUTPUT OF D.C.S. AND P.L.C.? PRINCIPLE AND WORKING OF HART? WHAT IS PNP AND NPN PROXY? CALIBRATION OF PRESSURE ,LEVEL ,FLOW SWITCH? DESCRIPTION OF FIELDBUS FOUNDATION? WORKING OF SOV.?
what is KV and XV valve