can we connect instrument earth pit to electrical earth
pit, if not why?
Answers were Sorted based on User's Feedback
Answer / jp
Normally, all instruments to be grounded to clean earth (should be less than 2 Ohms). Whereas Electrical earth resistance might be more than this. So Instrument earth pit to be seperate from electrical earthpit.
| Is This Answer Correct ? | 14 Yes | 6 No |
The internal screen is always floating at the instrument.
This means we just put some heat shrink on it to seal it and
then tie it off inside the instrument and just let it lie
there. The overall screen (braiding surrounding the cable
just below the pvc outside)will be in contact with the gland
once you have installed the gland. On the gland thread you
install a copper gland ring and a red IP washer, and the
gland then are attached to the instrument. From the gland
ring you use a six mm bolt and nut with copper washers to
attached a small diameter earth wire (about 4 to 6mm is
fine). This earth wire is then attached to the outside of
the instrument at the earth connection point on it's
housing. Every instrument will have this earth connector on
the outside of it's housing. From there you attached another
earth wire to the earth boss nearby. This boss is normally
just a piece of round bar about 40mm in diameter and about
30mm long and tapped in the middle that is welded to the
structure close by, specially for this earthing of the
instruments. Again it is better to use copper washers. If no
boss is available you can use some other point on the
structure as well like a stainless steel cable tray for
instance but the earth boss should really be part of the design.
On the other side of the instrument cable at the RTU the
internal screen in attached the instrumentation clean earth.
The dirty earth is used only for electrical equipment.
Good luck
| Is This Answer Correct ? | 2 Yes | 12 No |
if drum level is low what is interlock? i mean we put interlock to fd fan or id fan ?
OBJECTIVE TYPE QUESTIONS OF ANALYTICAL INSTRUMENTATION
0 Answers Fauji Fertilizer, GSECL, NFL, Power Plant,
Give Detail information about plc,dcs,and scada system?
i am confusing about differential pressure transmitter as i seen so many DPTs in different ranges how can we calculate level and flow with mmh20 plz tel me
Why Bently Nevada use negative voltage for vibration probes?
Which tank weighing system is better to install (Accuracy point of view) 1) Tank weighing system with 3 load cell or 2) Tank weighing system with 4 Load cell
how u measure flow?orifice measurement?why all ft in square root?
We Have Two Field bus Pressure Transmitters of Different Sensor Range (I.E One is of Lower range and Another is of Higher Range).Is same Process Line. My Question is Can i provide Saturation Limit to my field Bus Transmitter as We can provide Saturation current limit to HART Instruments. As During Low Pressure Both Working OK ,But During High Pressure, transmitter with Lower sensor range Goes to Fault mode as Beyond its Sensor Limit it can Measure, So may I provide Saturation point Some where to Suppress This Fault during High Pressure.
On drum level, why we are using air to close Control valve?
why are use only 4 to 20ma. signal.
What's the difference between cold loop test and hot loop test?
what is the reason while warning lamp is on while the engine is cranking?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)