Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


can we connect instrument earth pit to electrical earth
pit, if not why?

Answers were Sorted based on User's Feedback



can we connect instrument earth pit to electrical earth pit, if not why?..

Answer / jp

Normally, all instruments to be grounded to clean earth (should be less than 2 Ohms). Whereas Electrical earth resistance might be more than this. So Instrument earth pit to be seperate from electrical earthpit.

Is This Answer Correct ?    14 Yes 6 No

can we connect instrument earth pit to electrical earth pit, if not why?..

Answer / sam

The internal screen is always floating at the instrument.
This means we just put some heat shrink on it to seal it and
then tie it off inside the instrument and just let it lie
there. The overall screen (braiding surrounding the cable
just below the pvc outside)will be in contact with the gland
once you have installed the gland. On the gland thread you
install a copper gland ring and a red IP washer, and the
gland then are attached to the instrument. From the gland
ring you use a six mm bolt and nut with copper washers to
attached a small diameter earth wire (about 4 to 6mm is
fine). This earth wire is then attached to the outside of
the instrument at the earth connection point on it's
housing. Every instrument will have this earth connector on
the outside of it's housing. From there you attached another
earth wire to the earth boss nearby. This boss is normally
just a piece of round bar about 40mm in diameter and about
30mm long and tapped in the middle that is welded to the
structure close by, specially for this earthing of the
instruments. Again it is better to use copper washers. If no
boss is available you can use some other point on the
structure as well like a stainless steel cable tray for
instance but the earth boss should really be part of the design.
On the other side of the instrument cable at the RTU the
internal screen in attached the instrumentation clean earth.
The dirty earth is used only for electrical equipment.
Good luck

Is This Answer Correct ?    2 Yes 12 No

Post New Answer

More Instrumentation Interview Questions

if drum level is low what is interlock? i mean we put interlock to fd fan or id fan ?

4 Answers  


OBJECTIVE TYPE QUESTIONS OF ANALYTICAL INSTRUMENTATION

0 Answers   Fauji Fertilizer, GSECL, NFL, Power Plant,


Give Detail information about plc,dcs,and scada system?

0 Answers  


i am confusing about differential pressure transmitter as i seen so many DPTs in different ranges how can we calculate level and flow with mmh20 plz tel me

1 Answers  


Why Bently Nevada use negative voltage for vibration probes?

4 Answers  


Which tank weighing system is better to install (Accuracy point of view) 1) Tank weighing system with 3 load cell or 2) Tank weighing system with 4 Load cell

0 Answers  


how u measure flow?orifice measurement?why all ft in square root?

1 Answers  


We Have Two Field bus Pressure Transmitters of Different Sensor Range (I.E One is of Lower range and Another is of Higher Range).Is same Process Line. My Question is Can i provide Saturation Limit to my field Bus Transmitter as We can provide Saturation current limit to HART Instruments. As During Low Pressure Both Working OK ,But During High Pressure, transmitter with Lower sensor range Goes to Fault mode as Beyond its Sensor Limit it can Measure, So may I provide Saturation point Some where to Suppress This Fault during High Pressure.

0 Answers   OPaL,


On drum level, why we are using air to close Control valve?

4 Answers   L&T,


why are use only 4 to 20ma. signal.

9 Answers   Otsuka,


What's the difference between cold loop test and hot loop test?

5 Answers  


what is the reason while warning lamp is on while the engine is cranking?

0 Answers   Jindal,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)