Answer / sunil guru
the current rating is greater than the MCCB rating. so go for
higher current rating...
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / m v v s n murthy
Generally, we will distribute our 1 phase loads equally in 3
phases to get the balanced load and the circuit becomes star
connected. In star connection, there will be no current in
neutral line if the load is balanced.
In the lighting loads also we have to distribute equally in
3 phases. If not, current will increased in neutral.
In your case you did not devide the lighting load to get
balanced star connection, and also the neutral link in your
MCCB under size to carry unbalanced neutral current. And
also there may be loose connection at neutral link.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / sachin
Dear friend ,
First measure the current flowing thro MCCB .If it is MCCB
then it must have protective system . Set it as per max
current.measure the neutral current at full load. measure
neutal to earth voltage . most possible reasons are
1] Neutral link is undersized or
2] Loose connections
3] Neutral is not properly earthed .
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / anirudha
the mccb is burning because the rating for the current for
which it is selected may not be proper
| Is This Answer Correct ? | 0 Yes | 1 No |
what is formula for calculate thermal overload in new numiricalrelay( not in bimetal relay)?
why capacitor bank always connected in delta,why not in star to a system?
PLC Training in chennai | PLC Training institute in chennai, PLC Training center in chennai | Best PLC Training in chennai | PLC Training course in chennai | SCADA Training in chennai | PLC Training in india
what is ment by doublefield revolving theory?
if the 10 hp motor name plate indicates rated current as 13.6 amp the what will be the thermal relay setting? Why? And in how much time relay will trip at the set value?
Is it possible to operate a synchronous 2-poles turbogenerator with a still-in-place faulted bar but electrically disconnected ???? If yes, should I act on the other phases as well ???
Differentiate between digital phase converter and ordinary phase converter.
We have got the HT connection of 1000 KVA in which we have installed a seprate APFC panel at the PCC end & seprate KWH meter is installed. My question is that does the KWH reading shown in the meter is a part of the Consumption ???? ( approx 500 units is shown)
upto how many load can v connect to stabilizer which is used for tv
why rating of motor in HP?
WHAT IS THE ROLE OF ELECTRICAL & ELECTRONICS ENGINEER IN TCS.
What is ment by KVAR and what are the advantage&dis- advantages of KVAR
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)