What are the difference between off-load tap changer and
on-load tap changer in transformer?
Answers were Sorted based on User's Feedback
Answer / g.trinadh
In off load tap changing transformers tap is changed after discharging of load on LT side where as in on load tap changing transformers tap can be changed with out discharging load on transformer.
Is This Answer Correct ? | 17 Yes | 1 No |
Answer / vinoth kumar.n
In off load tap changer the transformer will be in off
condition,it safe for equipment and personal safety,,
In on load tap changer the transforme will be in running
condition,there is no interruption of power supply,but
there is unsafe for windings.
Now a days 230kv are and above prefering only off load tap
changer,The tap changer provision will be held on HT side
only.
Is This Answer Correct ? | 3 Yes | 7 No |
what is the difference b/w permitivity and permeability
Why are some relay circuts designed to have the ct current flow through the neutral instead of the phase wire, such as in some diff relays?
what is the minimum (Common factor) insulatin resistance of the following a, 4mm sq wire b, cable from 50 mm sq to 800mm sq
how we can varying the speed of dc motor ?
how to calculate transformer turn primary & secondary side 11kv to 420v
An electric bulb giving light but at the time of lighting which one it takes? voltage or current
i need circuit star delta connection?
What is the meaning of EDO in DG panels?
WHAT IS LINE TRAP,HOW IS IT FUNCTION?
Why all voltage level are multiples of 11, like 220V, 440V, 1100V instead of 200V, 400V, 1000V?
9 Answers Indian School of Mines,
hi how are you? i m in walchand college of engg. do you have interest in join me through email so send your email id
what is the 2MVA distribution transformer efficiency