without a positionar can a control valve operate? give the
difference of operating with positionar and without positionar?
Answers were Sorted based on User's Feedback
we can control the control valve accurately with the help of
positioner.
| Is This Answer Correct ? | 9 Yes | 0 No |
There are applications where the positioner is actually
causing the process to run away, due to the valve reacting
being too fast, and the control will be much easier without
the positioner. You can do this by installing a I/P
converter, piped directly to the actuator.
In 99,99% of applications however, the positioner is
necessary to control the process since process changes is
normally very fast and smooth control will be impossible
without a positioner to speed up the reaction time of the
control valve and keeping the process on the desired control
set-point.
In these applications if you do not install a positioner you
will find that your process runs in a big sinuous wave form
and this will obviously cause a major chain reactions
through out the whole plant.
Good luck
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / ramesh dham
There are two works of positionar First is to boost up the pneumatic signal to desired spring range of actuator and second is to get mechanical feedback of valve stem to accurate control over valve.
if we do not use positionar then our valves spring range must lie between 3-15 psig also we can't control accurately the process with higher variation.
| Is This Answer Correct ? | 6 Yes | 0 No |
Only the diaphragm actuator type control valves can be
operated without positioners provided that the spring range
of the actuator is within the range of control air pressure.
Cylinder actuator type control valves cannot be operated
proportionally without a positioner. only on/off can be
done.
With positioner we can achive the exact position of the
control valve with speed. If positioner is not there then
the actuation will be sluggish and we cannot get exact
postioning of control valve
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / guest
yes it will operate. but we have to see the actuator
pressure rating range between that range it will operate.
with positionar a valve can run smoothly but without a
positionar it will sluggish.
| Is This Answer Correct ? | 5 Yes | 4 No |
what is cems analyzer explain with principle and drawing ?
Can any one tell me what type of question asked for instrumentation and control interview panel??? pls mail ramashankar.goel@gmail.com
Why we not use 2-20Ma or 1-20Ma
I want to apply for the universities in US,but i got the GRE score of (650+300=950)TOEFL 69/120.Is this score sufficient for applying universities please i am married i need to go to US because my husband didn't get H1 yet.please send me suggestion
WHAT IS AN INTERLOCK SYSTEM ?? HOW THEY WORKs ?? WHERE IT IS USED ??? MAINLY ??
2 Answers TATA, Tata Steel Limited,
What is the start up procedure of desalter
what is the use of conrol cable..?
What is fault tolerent system
what is difference btween rotameter and orifice plate?
Explain the mechanism behind the turbine meter.
Wht is Dry Leg Calibration and Wet Leg Calibration?
compare the thermocouple and pyrometer,which one is the best?why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)