without a positionar can a control valve operate? give the
difference of operating with positionar and without positionar?
Answer Posted / kkrameshkumar
Only the diaphragm actuator type control valves can be
operated without positioners provided that the spring range
of the actuator is within the range of control air pressure.
Cylinder actuator type control valves cannot be operated
proportionally without a positioner. only on/off can be
done.
With positioner we can achive the exact position of the
control valve with speed. If positioner is not there then
the actuation will be sluggish and we cannot get exact
postioning of control valve
| Is This Answer Correct ? | 5 Yes | 0 No |
Post New Answer View All Answers
What is three element drum level control system why its better than single element?
Can any body tell me about SAP MAINTINANCE MODULE. WHAT IS its function and application. And study material Source about it. I shall be very thankful.
Draw a wheatstone bridge circuit showing supply, meter and 3 wire RTD connection
anybody having Qatar Petroleum questions for instrument Technician offshore ....please send me
what is zero and span ?
Specific gravity.
TEMPERATURE VARIATION FOR FREQUENTLY.
in differential pressure transmitter,min&max pressure range for hp&lp
model question paper of instrumentation for Jindal GET 2010.plz reply sudhanshukumar08@yahoo.com
What is the difference between working pressure and calibration pressure of a control valve
how to calculate control valve bonnet size?? or how to select its material?
I was working on calibrating turbidity transmitters endress+hauser at effluent polishing plant.We calibrated using NTU buffers.What happened is that when we immersed the sensor, everytime we raise and lower the sensor gradually, the reading will vary.my question is that is there any specifications on what is the required distance from the bottom of the container with buffer to the face of the sensor?Is it ok to install the sensor in a medium which has turbulence specially if bubbles are present?
What is instrumentation measurement?
why we use cascade control and feed foreword control in 3 element control of boiler drum ?what is feed forward and cascade control system ?
How to Calibrate Ultrasonic Level Transmitter in field