Answer / solomon
Dry leg calibration and Wet Leg Calibration are used for
closed and pressurized vessels level measurement.
Difference:
Wet leg calibration is used for vapourised liquid(which
will be condensated by atmosphere)level.In LP side
Tapping ,liquid filled .
Dry leg calibration for the liquid under pressurised
condition which will not be condensated.
| Is This Answer Correct ? | 80 Yes | 17 No |
Answer / spencer
Dry leg is where the low pressure side is vented to ATM.,
and the vessel is open to ATM. Wet leg is where the vessel
is closed and the low side is connectd to the top bridle.
With each type the "legs" wil be filled with an inert fluid
with a higher density then the fluid in th evessel all has
to be taken into consideration when calibrating
instruments. I can normally hit a percent error of 1
%. Hope this helped the guy has no idea what he is talking
about.
| Is This Answer Correct ? | 15 Yes | 19 No |
what are the pinciples & units of flow, level, temperature, pressure, quality.
Hi, am aniket, I got engineering degree in instrumentation and control, but as their were no job availabilities for engineer's post I started working as instrumentation technician I kuwait, so my question is is this technician's experience worth for getting the position of engineer?
1 Answers Almeer Technical Services,
use of split range ? where it is used ? in which control loop it is used ?
what is Instrumentation?
What is the use instrument barriers? Can you give me review materials about this?
how does we do bench calibration of a differential transmitter.
1)How many tpes of vibration probe and how many tpyes of vibration. 2)how we can calibrate a vibration probe with tk3 3)what is RMS value in vibration measuring application and how we calculate it.
how to calculate signal cable sizing? and multipair cable sizing??explain in brief?
full process of gas turbin?
what will be the output of the temparature transmitter if temp is 120 degre celcius.
1 Answers Base Automation, NTPC, PDO,
How to do gas analysers calibration in AUTO and Manually by using zero and span gas?
What is Fieldbus?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)