Answer / solomon
Dry leg calibration and Wet Leg Calibration are used for
closed and pressurized vessels level measurement.
Difference:
Wet leg calibration is used for vapourised liquid(which
will be condensated by atmosphere)level.In LP side
Tapping ,liquid filled .
Dry leg calibration for the liquid under pressurised
condition which will not be condensated.
| Is This Answer Correct ? | 80 Yes | 17 No |
Answer / spencer
Dry leg is where the low pressure side is vented to ATM.,
and the vessel is open to ATM. Wet leg is where the vessel
is closed and the low side is connectd to the top bridle.
With each type the "legs" wil be filled with an inert fluid
with a higher density then the fluid in th evessel all has
to be taken into consideration when calibrating
instruments. I can normally hit a percent error of 1
%. Hope this helped the guy has no idea what he is talking
about.
| Is This Answer Correct ? | 15 Yes | 19 No |
how we convert Mili ampere to temp txt,level txt,flow txt,pressure txt range value
how to check diode wheather it is working or not by using multimeter?
Give 2 application of quartz crystal used for process parameter measurement.
What is the difference between HMI and MMI?
IS IT POSSIBLE TO CALIBRATE A LEVEL TRANSMITTER INDICATOR(ABB) USING HART COMMUNICATOR.? I MEAN TO CHANGE FROM ONE UNIT TO ANOTHER WITHIN INDICATOR (EG. INCH TO FEET)...? PLZ NOTE THAT I HAVE MADE THE UNIT CHANGE IN TRANSMITTER USING HART COMMUNICATOR..BUT WHAT ABOUT THE INDICATOR..?
How to calibrate the control valve.
why relays are used with plc?
How to calibrate displacer type level transmitter (chemtrol make )for level measurement in hotwell , LP & HP heater ?
how to calibrate bubbler type level transmitter of rosemount make and how to set air flow according to the range.. give one calibration procedure with one example
Good Evening all.My question is - For a feed water line to an equipment if i need to measure the flow we will use orifice /magnetic/vortex depend on cost/spec.If i need to measure a ''Alarm''signal and ''Interlock'' from one point i think we can use orifice type in one location with 2 different tapping points - one for alarm and one for an interlock to flow valve..If in case i need to have both these signals(Alarm & interlock) from magnetic flow meter,is it possible??will 2 seperate sensors will be located inbuilt r we can program it ??..i thk we can have one transmitter with these 2 signals...need to know any technical issues are there?pls clarify
in a electronic controller why we are using 250 ohm resistance in input signal?is i/p is necessary in control valve when we are using electronic controller give details?
How to Calibrate Flammable gas detector in field
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)