We have laid the single core Armoured cable 7 nos ( 2 each
phase & 1 neutral ) to cater our electrical load .
the issue is though we have Glanded the cable both the end
also givan the earthing to the panel both the end we are
facing a heavy sparking at the gland side. what could be
the reason.
Answers were Sorted based on User's Feedback
Answer / shantanu mishra
This is definitely a case of improper earthing. The
substation earthing is poor. The panel and armoring of cable
need to be more strongly earthed. During normal conditions
there would not be any sparking butwhen there is any fault
on 11kv line nearby, the ground potential suddenly rises and
so the panel comes at a high potential and sparking take
place between panels and armoring of cables which are not
getting proper earth.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / shantanau mishra
Dear Virendra
have you found any solution to your problem. Pl share.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ahmed
Well,you need to check if you really need to glad the
cables from both side .Or check the type of glad is it
metal or non-metalic .
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rajesh
Use special gland (Gland with bush) at the panel(load side), but ensure the proper gland earthing in first side. The above situation is due to circulating current
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / abhishek mishra
Dear Virendra
if you are using CRCA gland plate for glanding then such problem may occur. If you are using single core cables then either use aluminium gland plate or make a thin cut hole to hole in CRCA gland plate
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / robertm
It sounds like you have a loop, check and see if the
neutral and the earthing cable are laid down on the same
bars. If this not the incoming service then that could
cause your problem.
| Is This Answer Correct ? | 0 Yes | 1 No |
Guys,
let me clear that the earthing is proper we get the value
0.1ohm. We have used double compress gland which is fixed
in proper way, there no such thing like looping, but still
the problem is there . please share what else can be the
cause ?
| Is This Answer Correct ? | 0 Yes | 1 No |
Draw the equivalent circuit of crystal oscillator?
What is the difference between MCCB & ACB Where it can be used
How to check the cable fault / hv test of transformer cable.
why doesnt the back emf hold the speed of unloaded series motor?
HOW TO CALCULATE S/C,O/C,E/F OF ACB.
In a star(primary) to delta(secondary) transformer,how you take the neutral point?
salam&hi, i need to know about how can i calculate an enough current for the new building before i submit it to the suppliers
what is consequences of neutral and earth connect?
How to calculate phase to phase difference in 33KV Line ,11KV Line etc.
differtiate between energy consevation and energy efficiency..
what is the maintain in ACB,VCB,MCB,MCCB breakers?
If I have a motor of 1MW with 6.6kv, running at 35% load, how can i save energy without reducing the load ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)