What is difference between A.C & D.C Resistance ?
Answers were Sorted based on User's Feedback
Answer / ashok
There is no polarity for resistance. In AC consider voltage
and in DC current should be consider
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / dileep t
The A.C resistance is always greater than D.C resistance.
A.C resistance is about 1.62 times D.C resistance. In D.C
the frequency is zero . Hence the total impedance of a line
will be only resistive.
z=R+XL
since f=0;XL=0
Z=R.
But in A.C f is not equal to zero. Hence Z will be large as
compared with D.C
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / suresh
d.c resistance is only resistance due to the virtue of
conductor property only, a.c resistance is due to both
virtue of conductor property and skin effect.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / blade
In AC the movement of electric charge periodically reverse.
In DC the movement of electric charge is only in one
direction.
| Is This Answer Correct ? | 5 Yes | 5 No |
Is a DC Transformer Possible? if Yes, Then Why, if not Then Why?
For 160kw motor what size of cable and material is needed.?
why generaotr rating is in kva and dc motor in kw?
What is the equipment used to control the generator output?
What are the protection schemes used for protection of transformers ?
3 Answers Engineers India Limited,
what is the principle of singkle phase energy meter?
If i=10+10sin314t then find the rms and average value of current with explain?
why corona loss is less with negative polarity?
If I fill the form of engineering services and I left the exam de to navoidable reasons . Will it counts my one attempt
on 22.03.2015 at 17:15hrs Y phase 66kV class Power Trf-2 Current transformer has flashed over and oil came out. The failed CT has been replaced on 24.03.2015 at 13:15hrs and the Trf has been charged in presence of RT Hassan after conducting the pre-commissioning tests. On the same day at 17:00hrs the commissioned CT has again flashed over and immediately the Trf has been isolated from power supply. It is confirmed the secondary is not opened and checked the earth integrity and is found ok. Here what would be the reason for the CT failure?
distribution is maximum done by a)radial b)network c) parallel d)b & c
We are planning to synchronized DG's with our captive plant in the event of black start of plant, but before sync we checked voltage of DG with our plant voltage and it varies from 5 V to 450 V. So in this condition how we can sync DG with plant ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)