What is the equipment used to control the generator output?
Answers were Sorted based on User's Feedback
Answer / surya
basically AVR i.e. Automatic Voltage Regualator is used to
Control the output of the generator.
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / bala
AVR - Maintain the output voltage according to the set
value and Governor - Maintain the output Frequency(speed)
according to the set value.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / pillay
What control are you talking about?As Suria and Bala has said
AVR controls the voltage and governor controls the speed.If power
output is the concern than you may have to say the over current
protections and if the fault current is of concern than earth
fault relays like wise there are so many devices to control the
generator output.
| Is This Answer Correct ? | 1 Yes | 0 No |
Why slip ring ind. motor power consumption is low compare to induction motor .same 90 kw motor used same load output
how make megger test for control cable like 12c x 1.5mm and what it apply voltage and test timing details.
why they charge more bill for low power factor rather than high power factor
how to decide the load on secondary of the tranformer
is EEE eligible for getting electrical supervisor certificate ? if yes then from which state i sud apply
what is metering cum synchronizing panel and how it is used?
what is preventive maintenance? and what is predictive maintenance? and what diffrence both?
what is the defination of 'Mass' & 'Weight'
what is the effect come when i changed the alternator exciter field winding DC palority(+ve & -ve)which is coming from AVR.
What are the special protection given for high capacity Motor, more then 10mw
Draw an S.L.D of the main panel for a hospital, showing meter position. Essential loads are: 1) Equipment load 100 KW 2) Critical load 500 KW 3) Life AID Safety load 400 KW 4) NON-Essential load 200 KW 5) Other service loads 200 KW Calculate and suggest the size of the transformer, size of main cable, capacitor bank, and calculate the capacity of an emergency load having above first three mentioned loads is supplied by an emergency generator.
WHY IS THE POWER FACTOR NOT MORE THAN UNITY.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)