What are the protection schemes used for protection of
transformers ?
Answers were Sorted based on User's Feedback
Answer / s naved masood
For Transformers lesser than 1000KVA
1. Overcurrent protection at HT(fuses or overcurrent relays)
2. Overcurrent protection at LT (LT Air circuit breaker)
3. Moisture protection (Breather with silica gel)
4. Overburden protection (Temperature gauge)
5. surge protection (surge arrestors)
6. Pressure relieve valves
For transformers equal to or above 1 MVA
1. Overcurrent (IDMT and High set char relays)
2. surge protection (surge arrestors)
3. Oil temperature indicators (alarm + trip)
4. Winding temp indicators (alarm + trip)
5. Oil surge relay
6. Pressure relieve valves
7. sudden pressure relays
8. differential Protection
9. Restricted earth fault protection
10. Overfluxing protection
11. Buchholz relay (alarm + trip)
Also there are various tests that are done as a part of preventive maintenence.
1. winding resistance
2. turns ratio
3. Tan delta
4. Dissolved gas analysis
5. Furon analysis
6. Sweep frequency responce analysis
7. Partial discharge
8. Magnetic balance
10. Megger testing
| Is This Answer Correct ? | 18 Yes | 0 No |
Answer / soms
for small Xmers(transformers)we use simple protective
devices i.e. fuses,for medium size we use overcurrent
relays, for large size Xmers we use differential protection
scheme recommended .
| Is This Answer Correct ? | 5 Yes | 1 No |
What is lifting power for 1 wb/m2 and 1 A magnet?
speed of an electric wave
Different STANDARDS (BS, IS, IEC etc) gives different informations on CT specification. How they correspons w r t each other (i.e I mean to say BS provides "knee point voltage" but IS does not, then how can i select CT)
what is mutual induction principle?
Explain what are inter-poles and why they are required in a dc machine.
why Lightning arrestor are made by 2 seperate stack of inslutor but why cvt are in single stack of insulator.
Why we use startor to the motor?
why two over current realy used in vcb.
why the vfd motor take current high in vfd panel then mcc panel.current in vfd panel=160A in 93%.and mcc panel it shows 130A. (132kw motor)
How can I calculate the fault level of a transformer. 1. If fault is 3phase fault 2. If fault is 1phase fault 3. If fault is 2phase fault Dear all geniouses, can you help me by giving answer. If anybody want to send something then mail me at "msalam_shahin@yahoo.com"
A 230 v dc series motor is connected to 230 V ac supply, then
i have completed deee and i've (June2012-feb 2015 experience in electrical maintenance in pvt ltd company.company having HT & LT electrical power.how to apply electrical C-license ,NOW I was resigned my job,what are requirements of applying for c-license
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)