Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


WHY 6.6KV MOTORS ARE STAR CONNECTED AND WHY NOT DELTA CONNECTED,

Answers were Sorted based on User's Feedback



WHY 6.6KV MOTORS ARE STAR CONNECTED AND WHY NOT DELTA CONNECTED,..

Answer / sudhakar

in star line voltage is equals to root three times of
phase voltage
due to this the effective voltage applied is less so the
current drawn by the machine is less in star than in delta

Is This Answer Correct ?    56 Yes 5 No

WHY 6.6KV MOTORS ARE STAR CONNECTED AND WHY NOT DELTA CONNECTED,..

Answer / s.k sahoo

to reduce the starting current. is it ok?

Is This Answer Correct ?    46 Yes 16 No

WHY 6.6KV MOTORS ARE STAR CONNECTED AND WHY NOT DELTA CONNECTED,..

Answer / sunil kumar sinha

^.^ KV motors are generally star connected because
insulation of winding of motor and interturn insulation is
much less because voltage across each turn in star winding
is much less (root three times) than the windings of delta
connections.
If 6.6 KV delta motor is to be manufactured the insulation
level will be much higher between turns as well as winding
as it will experience voltage level of 11 KV STAR MOTOR.
tHE SIZE OF MOTOR WILL BE BIGGER BECAUSE OF HIGH INSULATION
THICKNESS IN THE WINDING AND IT WILL BE COSTLY ALSO.

Is This Answer Correct ?    24 Yes 7 No

WHY 6.6KV MOTORS ARE STAR CONNECTED AND WHY NOT DELTA CONNECTED,..

Answer / k.atchuta rao

generally at the time of starting any FOR induction motor
we need to have less starting CURRENT. at the same time we
need high starting torque. in motors the relation between
torque and current is (TORQUE IS DIRECTLEY PROPESNALL TO
SQUEREE OF THE CURRENT)WHILE REDUCING STARTING CURRENT AT
THE SAME TIME WE NEED TO MAINTAIN TORQUE IN A COORECT
VALUE. IF U USE STAR CONNECTION AT THE TIME OF STARTING IT
WILL REDUCES STARTING CURRENT TO 1/3 AND STARTING TORQUE TO
1/3. BECAUSE OF GIVEN MOTOR IS SMALL RATTING THERE IS MUCH
NO DIIFFERENCE OF REDUCING STARTING TORQUE WITH RESPECT TO
CURRENT

Is This Answer Correct ?    10 Yes 4 No

WHY 6.6KV MOTORS ARE STAR CONNECTED AND WHY NOT DELTA CONNECTED,..

Answer / dd

As per Industrial practice, it is mandatory to run motors
greater than 200kW at medium voltages. These motors are
star connected to reduce voltage across each phase winding
to 1/root3. This reduces burden on the winding insulation
as starting time is longer.

Is This Answer Correct ?    2 Yes 2 No

WHY 6.6KV MOTORS ARE STAR CONNECTED AND WHY NOT DELTA CONNECTED,..

Answer / fahri

Say My Transformer is 11/6.6kV Ynd11 and the Motor is Star
Connected. Would this approach be safe for my Motor that is
connecting the Delta of the Transformer to the Star of the
Motor.

Is This Answer Correct ?    0 Yes 0 No

WHY 6.6KV MOTORS ARE STAR CONNECTED AND WHY NOT DELTA CONNECTED,..

Answer / mayur

FOLLOWING MAY BE THE REASON.
1. REDUCE THE STARTING CURRENT

JUST LIKE STAR / DELTA STARTER USED FOR CERTAIN MOTORS TO REDUCE THE STARTING CURRENT. THE APPLIED VOLTAGE ACROSS THE WINDING IN CASE OF DELTA CONNECTED MOTOR IS 1.73 TIMES THE STAR CONNECTED MOTOR. HENCE IN STAR CONNECTED MOTOR THERE IS A REDUCED VOLTAGE STARTING. SUBSEQUENTLY CURRENT IS ALSO REDUCED, HOWEVER THERE IS A SMALL EFFECT ON THE STARTING TORQUE SINCE TORQUE IS PROPORTIONAL TO SQUARE OF THE CURRENT WHICH MAY BE ACCEPTABLE.

ALSO SINCE LESS VOLTAGE IS APPLIED, THE INSULATION REQUIRED FOR HT MOTORS MAY ALSO REDUCE LEADING TO COST SAVING.

Is This Answer Correct ?    0 Yes 0 No

WHY 6.6KV MOTORS ARE STAR CONNECTED AND WHY NOT DELTA CONNECTED,..

Answer / keyur lakhani

because,in 6.6kv we reqiure high starting torque so that we use star connection and also line voltage=root of 3 *phase volage
and also in this motor we connect more load so current drawn by this motor is high so we reduce by star connection

Is This Answer Correct ?    0 Yes 0 No

WHY 6.6KV MOTORS ARE STAR CONNECTED AND WHY NOT DELTA CONNECTED,..

Answer / shri..

Because when starting the motor takes high inrush current.

We can use delta connection but before that star connection
required (Star/delta starter)

Is This Answer Correct ?    15 Yes 16 No

WHY 6.6KV MOTORS ARE STAR CONNECTED AND WHY NOT DELTA CONNECTED,..

Answer / saksh

In delta connection line voltage is egual phase voltage so
inrush current will be high in motor phase, due to this
star coneection is used to reduced the starting phase
current.

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

Which state of India had first started power reforms?

1 Answers  


why transformer is rated in kva?

2 Answers  


explain working of differential protection for a transformer?

1 Answers   BARC,


Actually I have a doubt on neutral and earth.we use Ac power without taking neutral by connecting to earth,but at that time does it affects on efficiency of any electrical components or no? If yes how?

0 Answers  


1.why motor rating in kw instead of KVA? 2.why alternators rating in KVA instead of KW?. 3.why transformer rating in KVA instead of KW?.

6 Answers  


i want to make an elec generater with only 12v car battery car alternater and 12 volt motor ..... will the battery charge and give power at same time with out over charging the battery?

1 Answers  


What is IDMT? What is the principle

3 Answers  


why induction motors are of lagging type and not leading type

9 Answers   Bhel,


what is the d/f b/w dol & star delta starter.

2 Answers  


single phase power supply give to separate one steel coup with water, what reaction create

0 Answers   Turbo,


explain the operating principles of CVT & RVT

2 Answers  


Give a brief idea about Control circuit wiring in Substation...???

2 Answers   KSEB,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)