Answer / sunil kumar sinha
In a three phase AC circuit, current is consetuted of
positive sequence, negative sequence and zero sequence
current.
the positive phase sequence current flows as perr the load
connected to the circuit. The negative phase sequence
current will flow due to diffence of three phase volages of
the system.If no difference of R Y B voltage is present,
the negative sequence current will not flow. The negative
phase sequence current present in the circuit will be of
same frequency but the phase sequence will be negative to
the system sequence. Negative sequence current will cause
excessive heating of generator rotor as the rotor will
experience double the system frequency so far the negative
sequence current is concerned. The zero sequence current is
present only in case of earth fault otherwise it is absent.
| Is This Answer Correct ? | 176 Yes | 16 No |
Answer / adil yousuf
Ans ; The negative phase sequence
current will flow due to diffence of three phase volages of
the system.If no difference of R Y B voltage is present,
the negative sequence current will not flow.
In rotating machines an unbalance voltage or current in one
phase winding due to elctrical faults or uneven load
further exacerbates the problem. The magnetic coupling
between the winding becomes uneven.
when subject to unbalance conditions, negative phase
sequence currents produce a counter rotating megnatic field
withrespect to the main field.
The resultant field rotates at double frequency and causes
underirable eddy-currents to flow in various structure such
as the machine rotor body , excitaation winding, stator end
winding and stator iron etc.
| Is This Answer Correct ? | 54 Yes | 8 No |
Answer / karma gyeltshen
An Negative Phase Sequence Current is usually caused by asymmetrical loading of the three phases, but may also be the an open-circuit phase (single-phasing).
An asymmetrical load on a generator produces a magnetic filed, which rotates in the opposite direction to the positive sequence field. The negative phase sequence flux induces currents in the rotor and these results in additional rotor losses and increased rotor temperature. The latter can represent a hazard for the rotor and this is the reason for applying NPS protection.
| Is This Answer Correct ? | 32 Yes | 0 No |
Answer / pradipto dhar
negative phase sequence is equally in magnitude, placed
apart 120 degree, rotate in oppsite direction to the
direction of phase sequence (RYB).
| Is This Answer Correct ? | 14 Yes | 22 No |
Answer / ravindra
as we know 3 phase fault is a balanced fault means after
having 3 phase fault on power sys , system remain balanced
but for the analysis of unbalanced fault like L-L, L-G etc
system not remain balanced(means phase difference between
currents of 3 phase not followes 120 degree). so for the
analysis of unbalnced fault another mathd is used . in ths
mthd we assume that we can write the unbalanced current or
voltage in three components 1 +sequence component 2. -ve
sequence component 3. 0 sequence .sum of all these 3
component =unbalanced fault. -ve srquence suggest for
opposite rotation or phase sequence
| Is This Answer Correct ? | 10 Yes | 21 No |
Answer / mukhesh
nag phase seq ismagnitude is same phase displacement is 120
electrical the phase seq of these components opposite of
original phase seq
| Is This Answer Correct ? | 9 Yes | 34 No |
Answer / puneet kumar
negative phase sequence is equally in magnitude, placed
apart 120 degree, rotate in oppsite direction to the
direction of phase sequence (RYB).
It is happen generally when load is
incresed, speed is reduce for some time then there is
happening of opposition of phase sequence due to increse of
load. (relative...)
| Is This Answer Correct ? | 9 Yes | 45 No |
Why motor is not calculated in kva, whereas transormers are calculated in kva
what is the principle of tubelight ??? what is the function of starter and choke ???
Safety of dry type transformer
when we design electrical schemes of 11/.415kv distribution..wen and were should we show the relays??what is the function of it?for example..we place EFR Relay CT between transformer neutral link and transformer earth.Like this what are the other type of relays we should use?why?where?Explain please..Thank you
PID controller details
why always out of the 3 phase(RYB) of supply, in Y phase w.r.t the voltage is higher? on R & B phase the voltage will be lower as compared to Y phase?
What is the different types of cable & current capacity of cable
how is working d.c amps meter?how to connect the dc ammeter inthe circuite?
what is transformer?
advantage of using 110v than 230v
what is ring system ?
Equal resistance of 100ohm each are connected to the arms of whestons bridge, which is supplied by 2v battery. The galvanometer can sense a current low as 1microAmp. What is the smallest resistance that can be measered.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)