Why motor is not calculated in kva, whereas transormers are
calculated in kva
Answers were Sorted based on User's Feedback
Answer / electrical ravi
Normaly Source is rated in KVA where as appliance/Load is
rated in KW.
Transformer converts product of V1 X I1 into V2I2, there is
no lead or lag pf at no Load, so the manufacturer specify
the rating of the transformer in KVA.
In motor, the electrical energy is converted to mechanical
energy and there is losses within the unit and there is
phase difference between voltage and current and thus
forming a builin power factor. So the manufacturer of motor
specifies the rating in KW with powerfactor value on its
name plate.
Is This Answer Correct ? | 9 Yes | 2 No |
what is mathematical relation between ac to dc current how will convert Iac=50amp to Idc
what are FM 200 systems? why it is useful for electrical systems ?
HOW THE OLTC TRANSFORMER SAVE ENERGY IN COMPARISON TO OFF LINE TRANSFORMER AND IS IT ECONOMICAL TO REPLACE THE OFF LINE TRANSFORMER TO OLTC TRANSFORMER
kindly arrange to send me RRB Bangalore previous question paper for JE/Electrical and JE/Signal I am going to write exam on 2010
what is threshold voltage for a relay???what does it exactly means ?whats its value in our indian transmission system say 11kv feeder RMU relay
What's voltage?
1 Answers Pakistan Atomic Energy Commission PAEC,
Mention the disadvantages of low power factor?
How do you determine the size of transformer radiators in a transformer?
difference between Ac and Dc mcb ????
if an induction motor is operated at unity power factor what will happen? will motor run or not? kindly describe a logical answer?
Is it possible to interlock between ACB & MCCB?
What is the stander resistance value between the neutral and earth?
10 Answers Crossdomain, Sepco,