warning lamp does not light, but it does light when the
wire from the lamp going to the sending unit is grounded
(the part that plugs into the sending unit) what does this
indicate)?
Answer / carl_ellis
If the lamp lights when the wire from lamp to the sending
unit is grounded, then the other side of the lamp has
power. The circuit is designed for the lamp to light when
the sending unit provides a complete electrical circuit.
The lamp lighting proves that
- the bulb is good
- there is power at the lamp.
If the warning lamp does not light when it should, then the
sending unit is faulty.
Carl Ellis
Measure First
Is This Answer Correct ? | 0 Yes | 0 No |
what is maximum vaccume?
what is the difference between CPC and i/p converter
if temperature transmitter is showing wran. sensor 2 fail how can you remove from the transmitter display m/n.3144p rosemount
what is the equation for gas flowmetering? whic includes gas flow, pressure, and temperature.
1. How many output signals do wew have in process control? 2. Could you write down the names of the pre-commissioning and commissioning stage test instruments and explain them (more than 5 items)? 3. What is the first step to commission a transmitter on service? 4. What is RTD? 5. Find the output value in MA of a temperature transmitter (RTD Type) at 120degree celius? 6. What is the O/P signal of a pneumatic transmitter? 7. What is the O/P signal of an elctronic transmitter? 8. What is the close loop and open loon?
this site is owned by an nonsense
what is mean of 3 by 2 automation ?
dear friends pls tell me how temperature compensations are done in bourdoun tube of pressure guages thankx
NSV type probe stands for
which type signal come control valve
uses of profibus?
How the flow can be measured by using DP Transmitter?