what is the difference between 3,4 wire RTD sensor?
Answers were Sorted based on User's Feedback
Your maths is not right but actually you are right, and the
temperature indication does not increase so significantly
that it is worth the effort to use a 3 or 4 wire RTD. It
might increase with something like 0,001Deg C so that is so
small you might as well say there is no difference in the
accuracy of a 2,3 and 4 wire RTD, using a local or smart
transmitter.
In the old days we use to use a 2 wire RTD in the field and
then run a cable say 200m to the temperature indicator. By
the time it gets to the indicator the temperature is
completely different from what it was in the field due to
the cable resistance that add itself the the RTD resistance.
We compensated for that by installing a 3de wire for the
sole propose to measure the resistance of the cable itself
and deduct that from the total resistance measured at the
temperature indicator.
So the actual resistance of the RTD as measured at the
temperature indicator is RTD - RLine1.(or [(Rline1/2)x2]if
you want)
With the 4 wire it makes it more accurate in that you can
now measure line one and line 2. The theory is that the one
line might have a small difference compare to the other line.
So the actual RTD resistance at the temperature indicator is
measured RTD - [(RLine1/2)+(RLine2/2)]
But since we all use the small compact local and smart
temperature transmitters these days, 3 and 4 wires are no
longer needed since the distance from the RTD to the
transmitter is only from about 50 to 500mm and but it seems
it have stayed due to some design engineer always saying,
why buy a 2 wire if you can get the 3 and 4 wire for just
about the same price. It will make the indication just more
accurate, but they never say by how much (0,001Deg C)
Good luck
Is This Answer Correct ? | 10 Yes | 2 No |
the difference between is that,the third wire for 3 wire
RTD is used for lead compensation.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / rajendraa
in 3 wire rtd lead wire resistance s reduced to a grt extent, lead wire error s such that t s the difference of wires A&B(A s the wire connected to rdt & B with the R in bridge circuit). in 4 wire rtd, the lead wire error s completely reduced,it s mainly used for calibrations & is very costly...
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / dinesh priyadarshi
RTD are used as 3 wire and 4 wire combination for following
reasons :
1) Lead wire compensation requird because this reduce the
error produce by the wire resistance
2) The distance also increae the error so to reduce the
errors we r using 3rth wire for lead compensation.
3) 3 wire and four wire lead compensation increase the
accuracy by means of resistance
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ng
there is lead resistance compensation in 3 wire RTD, where as 4 wire RTD is idle of lead resistance compensation as 2 wires are used for volt measurement and 2 wire for current measurement.there is no question of lead resistance error, it gives accurate result
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / niranjan
RTD is inherently a 2-wire device, A 2-wire RTD can be used with either a 3 or a 4 -wire instrument by jumping the appropriate terminals.3-wire instrument, a 4-wire RTD will not provide any better accuracy. If the fourth wire is not connected, the device is only as good as the 3-wire RTD; if the fourth wire is connected, new errors will be introduced. Connecting a 3-wire RTD to a 4-wire instrument can cause serious errors or simply not work at all, depending on the instrument circuitry.
Is This Answer Correct ? | 1 Yes | 14 No |
how the 2.5bar pressure able to control the 40bar steam
8 Answers IBM, PAFL, Thirumalai Chemicals,
How to calibrate DP tramitter in flow measurement application? consider my range of flow is 0 to 2000 kg/hr ? please give calculation of , How much pressure applied on low pressure side and high pressure side please give detail of calculation .... It so important for me please reply as soon as possible
Calculate the maximum pressure drop that can be allowed to occur across a control valve, so that we can prevent cavitation / flashing from occurring. Use the following formula: Δ P allow = Km (P1 – PvapourA) where, Δ P allow - the maximum allowable differential pressure for sizing purposes, or terminal pressure drop; Km- the valve recovery coefficient from the manufacturer’s catalogue; P1 - absolute inlet fluid pressure; PvapourA - absolute fluid vapour pressure at the inlet temperature; Use Atmospheric pressure = 101.3 kPa, P1 = 1200 kPa(g), PvapourA = 4 kPa, KM = 0.72
how to trim the pressure transmitter ?
dear sir we have insatlled positioner model no.sipart PS2 make Siemens at our control valves . now problem is if we want to increase the response of valve opening speedy /fast. what parameters do we change for positioner ? any idea. please guide us.
please send me hpcl placement papers
what do u mean by compensating?in power plant where are compensating done?how level , flow compensated?
what is the characteristics of control valve?
the square root type transmitter r used to which applications
What is Burnout feature in a recorder?
what is wave length were using ?
Flame scanner