Answer / shri..

As per my knowledge,
On my site bellow capacitor bank I am using.
I have 350 Kvar capacitor bank in this bank 25 kvar
capacitors are placed.

Capacitor specification

Volt = 440
Kvar = 25
Three Phase

KVA
I = ----------
Volt *1.732

25000
I = ----------
440 *1.732

I = 32.80 Amps


Eg 30 Kvar

KVA
I = ----------
Volt *1.732


30000
I = ----------
440 *1.732


I = 39.36 Amps

Is This Answer Correct ?    395 Yes 162 No

What the capacitor Current formula?, For 1 KVAr how amps its required? for using the KVAr for boos..

Answer / prakesh

Kvar= 1.73*V*I*Sin$ ($ IS INSTESD OF PHASE ANGLE PHI)

so I= kVAR/1.73*V*SIN$

IN A PURELY CAPACITIVE CIRCUIT $ IS 90 DEGREE
SO TERM SIN 90 = 1
HENCE WE CAN CALCULATE CAPACITOR CURRENT BY kVAR/1.73*V

Is This Answer Correct ?    127 Yes 15 No

What the capacitor Current formula?, For 1 KVAr how amps its required? for using the KVAr for boos..

Answer / pasuvaraj

You explained the answer in KVA? where do get the kva from
this variables, the formula for capacitor in KVAr, KVAr
into KW, KVA & Amps

Is This Answer Correct ?    88 Yes 26 No




What the capacitor Current formula?, For 1 KVAr how amps its required? for using the KVAr for boos..

Answer / utkarsh

Its 1.3A/KVAR

Is This Answer Correct ?    57 Yes 15 No

What the capacitor Current formula?, For 1 KVAr how amps its required? for using the KVAr for boos..

Answer / mehmud ahmed

Hi every one how are you
if u need to know three phase capacitor rating than

I= kvar x 1000 / V x 1.73

Example:

i have 25 Kvar capacitor and line to line voltage is 440. i want to know current rating of capacitor

I = KVAR x 1000 / V x 1.73
I = 25 x 1000 / 440 x 1.73
I = 25000 / 762.08
I = 32.80 Amp

So my Ans is (32.80 Amp)

Is This Answer Correct ?    43 Yes 2 No

What the capacitor Current formula?, For 1 KVAr how amps its required? for using the KVAr for boos..

Answer / jose

VOLT = 400
KVAr = 30
PHASE = 3

I = KVAr
-----
400 x 1.732
=43amps.
Kw = I x 0.624
= 26.8KW.

Is This Answer Correct ?    56 Yes 37 No

What the capacitor Current formula?, For 1 KVAr how amps its required? for using the KVAr for boos..

Answer / muhammad umar

Calculate Size of Capacitor Bank / Annual Saving & Payback Period




APRIL 1, 2014 9 COMMENTS
Calculate Size of Capacitor Bank Annual Saving in Bills and Payback Period for Capacitor Bank.
Electrical Load of (1) 2 No’s of 18.5KW,415V motor ,90% efficiency,0.82 Power Factor ,(2) 2 No’s of 7.5KW,415V motor ,90% efficiency,0.82 Power Factor,(3) 10KW ,415V Lighting Load. The Targeted Power Factor for System is 0.98.
Electrical Load is connected 24 Hours, Electricity Charge is 100Rs/KVA and 10Rs/KW.
Calculate size of Discharge Resistor for discharging of capacitor Bank. Discharge rate of Capacitor is 50v in less than 1 minute.
Also Calculate reduction in KVAR rating of Capacitor if Capacitor Bank is operated at frequency of 40Hz instead of 50Hz and If Operating Voltage 400V instead of 415V.
Capacitor is connected in star Connection, Capacitor voltage 415V, Capacitor Cost is 60Rs/Kvar. Annual Deprecation Cost of Capacitor is 12%.
 Calculation:




For Connection (1):
Total Load KW for Connection(1) =Kw / Efficiency=(18.5×2) / 90%=41.1KW
Total Load KVA (old) for Connection(1)= KW /Old Power Factor= 41.1 /0.82=50.1 KVA
Total Load KVA (new) for Connection(1)= KW /New Power Factor= 41.1 /0.98= 41.9KVA
Total Load KVAR= KWX([(√1-(old p.f)2) / old p.f]- [(√1-(New p.f)2) / New p.f])
Total Load KVAR1=41.1x([(√1-(0.82)2) / 0.82]- [(√1-(0.98)2) / 0.98])
Total Load KVAR1=20.35 KVAR
OR
tanǾ1=Arcos(0.82)=0.69
tanǾ2=Arcos(0.98)=0.20
Total Load KVAR1= KWX (tanǾ1- tanǾ2) =41.1(0.69-0.20)=20.35KVAR
For Connection (2):
Total Load KW for Connection(2) =Kw / Efficiency=(7.5×2) / 90%=16.66KW
Total Load KVA (old) for Connection(1)= KW /Old Power Factor= 16.66 /0.83=20.08 KVA
Total Load KVA (new) for Connection(1)= KW /New Power Factor= 16.66 /0.98= 17.01KVA
Total Load KVAR2= KWX([(√1-(old p.f)2) / old p.f]- [(√1-(New p.f)2) / New p.f])
Total Load KVAR2=20.35x([(√1-(0.83)2) / 0.83]- [(√1-(0.98)2) / 0.98])
Total Load KVAR2=7.82 KVAR
For Connection (3):
Total Load KW for Connection(3) =Kw =10KW
Total Load KVA (old) for Connection(1)= KW /Old Power Factor= 10/0.85=11.76 KVA
Total Load KVA (new) for Connection(1)= KW /New Power Factor= 10 /0.98= 10.20KVA
Total Load KVAR3= KWX([(√1-(old p.f)2) / old p.f]- [(√1-(New p.f)2) / New p.f])
Total Load KVAR3=20.35x([(√1-(0.85)2) / 0.85]- [(√1-(0.98)2) / 0.98])
Total Load KVAR1=4.17 KVAR
Total KVAR=KVAR1+ KVAR2+KVAR3
Total KVAR=20.35+7.82+4.17
Total KVAR=32 Kvar
 Size of Capacitor Bank:




 Site of Capacitor Bank=32 Kvar.
Leading KVAR supplied by each Phase= Kvar/No of Phase
Leading KVAR supplied by each Phase =32/3=10.8Kvar/Phase
Capacitor Charging Current (Ic)= (Kvar/Phase x1000)/Volt
Capacitor Charging Current (Ic)= (10.8×1000)/(415/√3)
Capacitor Charging Current (Ic)=44.9Amp
Capacitance of Capacitor = Capacitor Charging Current (Ic)/ Xc
Xc=2 x 3.14 x f x v=2×3.14x50x(415/√3)=75362
Capacitance of Capacitor=44.9/75362= 5.96µF
Required 3 No’s of 10.8 Kvar Capacitors and
Total Size of Capacitor Bank is 32Kvar
 
 Protection of Capacitor Bank




 Size of HRC Fuse for Capacitor Bank Protection:
 Size of the fuse =165% to 200% of Capacitor Charging current.
Size of the fuse=2×44.9Amp
Size of the fuse=90Amp
 Size of Circuit Breaker for Capacitor Protection:
 Size of the Circuit Breaker =135% to 150% of Capacitor Charging current.
Size of the Circuit Breaker=1.5×44.9Amp
Size of the Circuit Breaker=67Amp
Thermal relay setting between 1.3 and 1.5of Capacitor Charging current.
Thermal relay setting of C.B=1.5×44.9 Amp
Thermal relay setting of C.B=67 Amp
Magnetic relay setting between 5 and 10 of Capacitor Charging current.
Magnetic relay setting of C.B=10×44.9Amp
Magnetic relay setting of C.B=449Amp
 Sizing of cables for capacitor Connection:
 Capacitors can withstand a permanent over current of 30% +tolerance of 10% on capacitor Current.
Cables size for Capacitor Connection= 1.3 x1.1 x nominal capacitor Current
Cables size for Capacitor Connection = 1.43 x nominal capacitor Current
Cables size for Capacitor Connection=1.43×44.9Amp
Cables size for Capacitor Connection=64 Amp
Maximum size of discharge Resistor for Capacitor:
 Capacitors will be discharge by discharging resistors.
After the capacitor is disconnected from the source of supply, discharge resistors are required for discharging each unit within 3 min to 75 V or less from initial nominal peak voltage (according IEC-standard 60831).
Discharge resistors have to be connected directly to the capacitors. There shall be no switch, fuse cut-out or any other isolating device between the capacitor unit and the discharge resistors.
Max. Discharge resistance Value (Star Connection) = Ct / Cn x Log (Un x√2/ Dv).
Max. Discharge resistance Value (Delta Connection)= Ct / 1/3xCn x Log (Un x√2/ Dv)
Where Ct =Capacitor Discharge Time (sec)
Cn=Capacitance  Farad.
Un = Line Voltage
Dv=Capacitor Discharge voltage.
Maximum Discharge resistance =60 / ((5.96/1000000)x log ( 415x√2 /50)
Maximum Discharge resistance=4087 KΩ
Effect of Decreasing Voltage & Frequency on Rating of Capacitor:
 The kvar of capacitor will not be same if voltage applied to the capacitor and frequency changes
Reduced in Kvar size of Capacitor when operating 50 Hz unit at 40 Hz
Actual KVAR = Rated KVAR x(Operating Frequency / Rated Frequency)
Actual KVAR = Rated KVAR x(40/50)
Actual KVAR = 80% of Rated KVAR
Hence 32 Kvar Capacitor works as 80%x32Kvar= 26.6Kvar
Reduced in Kvar size of Capacitor when operating 415V unit at 400V
Actual KVAR = Rated KVAR x(Operating voltage / Rated voltage)^2
Actual KVAR = Rated KVAR x(400/415)^2
Actual KVAR=93% of Rated KVAR
Hence 32 Kvar Capacitor works as 93%x32Kvar= 23.0Kvar
Annual Saving and Pay Back Period




 Before Power Factor Correction:
 Total electrical load KVA (old)= KVA1+KVA2+KVA3
Total electrical load= 50.1+20.08+11.76
Total electrical load=82 KVA
Total electrical Load KW=kW1+KW2+KW3
Total electrical Load KW=37+15+10
Total electrical Load KW =62kw
Load Current=KVA/V=80×1000/(415/1.732)
Load Current=114.1 Amp
KVA Demand Charge=KVA X Charge
KVA Demand Charge=82x60Rs
KVA Demand Charge=8198 Rs
Annual Unit Consumption=KWx Daily usesx365
Annual Unit Consumption=62x24x365 =543120 Kwh
Annual charges =543120×10=5431200 Rs
Total Annual Cost= 8198+5431200
Total Annual Cost before Power Factor Correction= 5439398 Rs
 After Power Factor Correction:
 Total electrical load KVA (new)= KVA1+KVA2+KVA3
Total electrical load= 41.95+17.01+10.20
Total electrical load=69 KVA
Total electrical Load KW=kW1+KW2+KW3
Total electrical Load KW=37+15+10
Total electrical Load KW =62kw
Load Current=KVA/V=69×1000/(415/1.732)
Load Current=96.2 Amp
KVA Demand Charge=KVA X Charge
KVA Demand Charge=69x60Rs =6916 Rs————-(1)
Annual Unit Consumption=KWx Daily usesx365
Annual Unit Consumption=62x24x365 =543120 Kwh
Annual charges =543120×10=5431200 Rs—————–(2)
Capital Cost of capacitor= Kvar x Capacitor cost/Kvar = 82 x 60= 4919 Rs—(3)
Annual Interest and Deprecation Cost =4919 x 12%=590 Rs—–(4)
Total Annual Cost= 6916+5431200+4919+590
Total Annual Cost After Power Factor Correction =5438706 Rs
 Pay Back Period:




 Total Annual Cost before Power Factor Correction= 5439398 Rs
Total Annual Cost After Power Factor Correction =5438706 Rs
Annual Saving= 5439398-5438706 Rs
Annual Saving= 692 Rs
Payback Period= Capital Cost of Capacitor / Annual Saving
Payback Period= 4912 / 692
Payback Period = 7.1 Years

Is This Answer Correct ?    18 Yes 0 No

What the capacitor Current formula?, For 1 KVAr how amps its required? for using the KVAr for boos..

Answer / arnie

For correcting PF KVAr is introduced, thus formula

pf=cos A is significant

there you should have a desired PF. If for example you need
a power factor of .90 to maintain for a 30kVAR the watts
that would come will be:

A=arccos .90
A= 25.84

WATTs= KVAR/tan 25.84

= 62500 watts approx.

remember that for PF correnction it is the KVAR that is in
need of computation and not the watts so the question would
rather be, how much capacitor kVAR you need to correct the
power factor.

Is This Answer Correct ?    40 Yes 24 No

What the capacitor Current formula?, For 1 KVAr how amps its required? for using the KVAr for boos..

Answer / harry

The question requires more details.
First the "K" represents kilo or 1000.
The real power (kW) can be thought of as the x-axis and the
reactive power (kVar) from inductance or capacitance can be
thought of as the y-axis. The hypotenuse is the
Apparent power (KVA). The relationship of Real to apparent
power gives the Power Factor, where a power factor of 1.0
simply means that you only have real power, no reactive
power. The leading and lagging VARs from capacitance and
inductance, respectively can be added numerically since
they are on the same axis.
To ask, how muck kVars are required for a given kW doesn’t
make a lot of sense because you need to include the desired
power factor.

Is This Answer Correct ?    24 Yes 11 No

What the capacitor Current formula?, For 1 KVAr how amps its required? for using the KVAr for boos..

Answer / 9561354591

** Capacitor Current formula is

I= kVAr/kV/1.732 ( for 3 ph capacitor )

**for 1 kVar capacitor... suppose voltage is 440 volts than,

I=1/0.440/1.732
I=1.31 Amps.

For all your information,generally 1 kVAr capacitor takes
0.5 watts...henceforth..

30 kvar capacitor required kw=30X0.5=15 watts and is 0.015kw

thanks!!!!!!!

Is This Answer Correct ?    23 Yes 14 No

Post New Answer



More Electrical Engineering Interview Questions

what does kirlosker deals with?

3 Answers  


In separetly excited m/c,we excite the field by a dc source,what not with ac source?

2 Answers  


dear all, How do i increase UPS (1000VA)backup time ? i have connected 2 12v wold you please 120 aH battery externally. ups charge the lead acid battery only 12.7 volt. backup time only 10.00 minuts and gose off. can any one of you help me?

1 Answers   ups, Technomax,


how we calculate electrical load on a building according to area?

0 Answers   HFCL,


FOR WHICH FAULTS OR CONDITIONS DOES A TRANSFORMER DIFFERENTIAL PROTECTION DOES NOT OPERATE???

10 Answers  






What will hapen if we connect more capacitors than required for powerfactor control? Exactly what will be the effect on power system?

2 Answers   Mandovi Pellets,


why a tester wont shock while testing the power in house

0 Answers   Tessolve,


Can u explain : what is supply for train (whether a,c or d.c ).I know that supply is 25000v a.c .But there is rumour that supply is D.C. And also explain how lights and fans inside the trains are working ,and what type of motors are used in trains whether D.C motors or induction motors .If d.c motor, how it gets supply.If traction motors are used then what are traction motors and its functions and how it differs from other motors and also explain about locomotive . y d.c series motor in train.train wheels r driven by D.C shunt motor ,at what voltage,and at what speed. please reply..............

0 Answers  


A commercial Building is designed with 14th floor levels with indoor substation of three phase transformer with rated capacity of 1000 Kva.The transformer delivered 65% of its rated capacity at 0.67 power factor lagging.Because of low power factor, the power customer was penalized and certain cost was charged accordingly based on every point percentage lower than 85%.This situation may repeatedly happen on the succeding energy bills of power customer.The power customer is desired to improve its historical power factor of 0.67 lagging and no further penalty be impose by the local power company on the next bill. Q: Identify the appropriate solution you want to offer to Client?.Justify SCIENTIFICALLY and MATHEMATICALLY the principles behind the solution.

0 Answers  


want to know about DMRC

4 Answers  


What are the maximum and minimum ratings of MCB,MCCB,ACB,OCB,VCB and SF6 breakers?

2 Answers   ABB, SK E&C, Sodexo,


if a.c supply is given to the motor,, what happen?

0 Answers   MSEB, Bhel, L&T,






Categories
  • Civil Engineering Interview Questions Civil Engineering (4635)
  • Mechanical Engineering Interview Questions Mechanical Engineering (3700)
  • Electrical Engineering Interview Questions Electrical Engineering (15765)
  • Electronics Communications Interview Questions Electronics Communications (2636)
  • Chemical Engineering Interview Questions Chemical Engineering (762)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (79)
  • Bio Engineering Interview Questions Bio Engineering (30)
  • Metallurgy Interview Questions Metallurgy (95)
  • Industrial Engineering Interview Questions Industrial Engineering (199)
  • Instrumentation Interview Questions Instrumentation (2879)
  • Automobile Engineering Interview Questions Automobile Engineering (171)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (41)
  • Marine Engineering Interview Questions Marine Engineering (62)
  • Power Plant Engineering Interview Questions Power Plant Engineering (169)
  • Engineering AllOther Interview Questions Engineering AllOther (1334)