What the capacitor Current formula?, For 1 KVAr how amps
its required? for using the KVAr for boosting the PF Design
Calculation.( Eg: for 30 KVAr required how many KW?)
Answer Posted / arnie
For correcting PF KVAr is introduced, thus formula
pf=cos A is significant
there you should have a desired PF. If for example you need
a power factor of .90 to maintain for a 30kVAR the watts
that would come will be:
A=arccos .90
A= 25.84
WATTs= KVAR/tan 25.84
= 62500 watts approx.
remember that for PF correnction it is the KVAR that is in
need of computation and not the watts so the question would
rather be, how much capacitor kVAR you need to correct the
power factor.
| Is This Answer Correct ? | 40 Yes | 24 No |
Post New Answer View All Answers
how to calculate mf when meter and cTPT detail are given
How does a battary stores charge in it? please explain in simple manner and in detail.thanks
What is Plank's Law?
What information we need to prepare relay coordination chart
How many turns are there in primary winding? (In Transformer)
What do you mean by the zone of protection?
What are the different types of transformers?
What is the real function of reverse power relay in generator panel while syncronising?
Explain how you decide what size of electrical wire do you need?
how to decide the panel size like MDB ,SMDB PANEL SIZES
What is highest size of HT motor like 11 kv or 33 kv,and how to make it 750 rpm.i think the size will be very big.any idea ? pl. reply..
what is the transformer rush current?
What is effect of harmonic current (Draw by VFD) on power system/ electrical Equipments ?
kindly send me 11KV MV motor differential protection procedure by primary injection method.
reason of diode failure in alternator