What the capacitor Current formula?, For 1 KVAr how amps
its required? for using the KVAr for boosting the PF Design
Calculation.( Eg: for 30 KVAr required how many KW?)
Answers were Sorted based on User's Feedback
Answer / sagar
Q = VIsin(fi)
capacitor current = I = Q/Vsin(fi)
For , 230 v and power factor angle 90 ,then
I = 1/230*sin 90 = 4.32 amp.
If power factor angle is 36.89 (power factor 0.8)
,then
P/Q = kw/KVAR = VIcos(fi)/VIsin(fi)
P/Q = cos(fi)/sin(fi) = Tan(fi)
P = Q tan(fi)
P = 30 tan(36.89) = 30 * 0.75 = 22.5 Kw
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / kalanidhi
Current calculation for 200 kvar capacitor
CAPACITOR VOLTAGE CALCULATION
#System Voltage (MV) : 433V (WITH +- 5%)
#Voltage drop across (Maximum) : 433 x -5% = 21.65V
Capacitors working : 411.35 Volts.
CAPACITOR CURRENT CALCULATION
KVAR Calculation at 433 Volts.
KVAR 433 Volt (433)2
= ------------ 200KVAR
(411.35)2
187489
= ----------- 200 KVAR
169208
= 1.1 x 200 KVAR = 221.59
= 221.59 KVAR
Current for 221.56 KVAR at 433 V = 221.59
------------------------ x 1000
433 x 1.732 x 0.6
= 492 Amps.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mohammad rafique
dear,sir
my answer is 1 kvar = 1.3122 will be
my 2nd answer is 30 kvar= 44.5 kw will be and the mantioned
by powr factor like this,current cos(f1)and (requred cos(f2)
if my answer is correct then i shall be obligged to you
Is This Answer Correct ? | 3 Yes | 3 No |
Answer / prasenjit chowdhury
Full load current 350 Amps, Line Voltage 430. 1 KVAR = How many Amps. What is the formula or calculation to sagest the capacitor seating on load.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / srinu
Kvar: 1.732* v*i
1kvar=1000var
I=1000/1.732*415 for three phas
I=1.392amps
Is This Answer Correct ? | 4 Yes | 5 No |
Answer / venkatesh o
normally Formula
Kvar= 1.732*V*I*Sin(pi)
If Pure Capacitor 90 Leads so The power factor is Unity(1)
Assume *V=415
*Sin(90)=1(But Reactive power is zero)
since I=Kvar/1.732*V*1 Eg. 1000/1.732*415*1=1.39A
other formula for Determine KW=KVAR/tan(pi)or KW=VIcos(PI)
Assume * cos(0.9)
since KW=KVAR/tan....Equ 1, take the cos invesr is equal to (0.9)=25.8419 ...Equ 2
KW=30KVAR/tan25.8419=61.94KW OR
they are more formulas
* KW=KVAR/tan(pi)
* Kw=KVA*cos(pi)
* Kw=SQroot(KVAZ^2-(KVAr)^2
Is This Answer Correct ? | 3 Yes | 5 No |
Answer / botsar joseph antony
Ic=IsinQ1-I'sinQ2
where Q1 = phi1 and Q2 = phi
I is the curent, before correction and I' is the current,
after correction.
Ic is the subject of formula.
Is This Answer Correct ? | 1 Yes | 7 No |
how to calculate slip ring induction motor stator and rotor currents??
if voltage bt phase & nutral is 38v in a panel board . whats the root cause.
how can synchronous generator can be used as synchronous condenser?
Define norton equivalent circuit?
How to test Power Transfomer vector group?
what is neutral grounding? why is it required? what is neutral grounding resistor and how is its value calculated??
what is reactive power and active power
sir, i am 3 years diploma course pass out candidate.what type of certificate can i got in marine service.
WHAT IS THE CURRENT CARRYING CAPACITY OF 2.5/3 CORE HI TUFF CABLE,WILL IT SAFLEY CARRY 8.6 AMPS OVER 120 METRES,CAN YOU ALSO ANSWER WITH FORMULA FOR WORKINGS OUT ,THANK YOU 3RDYR APPRENTICE.