if we want ot select cable size with reference to load
current it take than what is the formula and it is same for
aluminium or copper?
Answers were Sorted based on User's Feedback
Answer / mahesh sali
while selection of cable u should followed the below steps ;
1) cal. the full load current If.L= ( kw / 1.732 x v x
p.f. )
Assume the voltage drop of system as per application says
for motor it should be 10% Vd = 10%
2) Vd = ( 10/100) * v
3) Vd/ph. = ( Vd/1.732 )
4) R = vd/ph./IF.L
5) R-Rho*L/A
Assume , for Copper cable Rho = 1.72 e-8 Ohm-m
L = Length of cable
Base on the above assumation u can easily cal. the size of
cable.
After cal. the cable size , add. 25% extra in ur cal. the
cable size .
Thanking u
Is This Answer Correct ? | 2 Yes | 0 No |
In case of transformers, for copper cable 2.5A/sq mm and Al
i.5A/sq mm ,for generators 1.5A/sq mm and 1 A/sq mm
respectively.For others 4A & 2.5A per sq mm
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / naveen perugu
for copper cable 4Amps/Sqmm is the standard practice and
for alluminium 3Amps/sqmm is the standard practice for
safer operations
Is This Answer Correct ? | 4 Yes | 8 No |
what is the preventive @ predective maintenance
what is 400kv doble circuit quadpole tower?
difference between diode and scr?
single sphase energy meter measur
On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Current: 693A Voltage:294/20KV OLTC Type: T III Y1000 110/c 12193w Max Operation Current: 295A Step Voltage: 550V Arrangement in Tx windings: Y Connection Problem: Damage of Unit 1 Generator Transformer On Load Tap Changer (OLTC) Description of Incident: 9.00 a.m. :- Generator No Load test on excitation system started 10.30 a.m :- Carried out AVR change over test 11.30 a.m :- Preparation for Generator Manual Synchronizing test 12.00 a.m :- Manual Synshronizing test started. Observed incoming generator voltage higher than running voltage. CECR operator operated Generator Transformer OLTC to bring down the incoming generator voltage 12.03 a.m :-Generator Transformer abnormal alarm operated at Gen.Control Desk (CECR) CECR operater at Generator transformer bay informed that the transformer oil splashed out from OLTC. CECR operater informed that he heard explosion inside OLTC. Observed Oil level & Oil Flow alaram operated at Tranformer local annunciator. 12.05 am :- CECR operator 'Open Gen Field Breaker” 12.10 a.m. :- Elec1 team inspected the OLTC and found the OLTC rupture disk was broken and oil spilled at OLTC area. - Elec1 found the OLTC top cover bulging. Do anyone know why and possibility cause happen in this OLTC.
How are load losses and no-load losses measured at site in a DG set?
what is the effect of leading power factor
3 Answers Aurobindo, R L Steels and Energy,
What do you mean by class of CTs and what is the meaning of cl 1.0, cl5P10, cl 10P10 CTs?
Assume a condition such that two motors of rating 6.6kv,415v are connected to blower,so tell me which motor draw large current give appropriate reason?
What is the technical name of minute currents that i have been produced in moving electrical objects?
What is potientometer.How it is useful in a sychronoscope.
What is the difference between PLC & DCS?