What is the standard height for stancion supports? and what
is the standard mounting height for different transmitters?
Answers were Sorted based on User's Feedback
Answer / pragati sutar
Height of stanction should be about 1.2 to 1.5m (i.e same as
height of human being) so that operator can take reading of
transmitter easily.
| Is This Answer Correct ? | 18 Yes | 3 No |
Answer / vinoth kumar.n
maximum 1.2m to 1.5m standerd height for stancion
supports.because easy checking and maintanence purpose.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / yousuf
the standard height of the stanchion is 1350mm to 1500mm.At
this height only the maintenance crew can easily view the
transmitter.
(saudi aramco standard is 1500mm)
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / va
1.2 meter or the height of the dispaly shpuld match the eye
sight of the operator/user.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / toji james
The standard height of a stanchion support is a 1.5 meter
exactly.....
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / thomas
Hey sorry this is a query regarding the same matter.
Why is it 1.3 to 1.5 lower than the average ht of an operator, will this be helpful for maintenance.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / bert
Base on experience in a construction company, we mount the
stanchion support for any of the instruments on field, it
should be mounted at the height of 4.2 feet and it should
be free for all any obstruction for maintenance crew.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / sridhar
The height of stanchion is a 1.5 mtr due to if any
pressure,level tranx get any leakeage,that time no any
accident accour in eye face area
| Is This Answer Correct ? | 0 Yes | 3 No |
What is the difference between dry contact and wet contact?
What are the type of bonnets in the control valves?
what r all the type of viberation measurement measuring in turbin? what's the output of viberation sensor?
Explain the working of an enraf level gauge.
suppose, after calibrating a transmitter we fixed it in a process line. At live zero condition the Tx shows 4.5 mA. what should we do to make the Tx show 4 mA? If we adjust zero, will it not affect the calibration?
whats the problem will arrise if we rotate the hosing screw of the differential pressure transmitter?
find the kp ki kd from the transper function G(S)=29.44s+04707/1.5349s2+s
WE Know that different supply voltage of solenoid valve like 24,110,220 etc..how we check the solenoid supply is 24v or 220 NOTE: No specification at device.
what is the function of a diaphragm?
how u meassure room temp?is it possible 2 meassure room temp by rtd or thermocouple?between rtd n thrmocouple which is more regard?3 meassure diff. between rtd n thermocouple?
any body please send me the old question papers of ongc test.
capillary type tranmitter using remote seals and capillary tubes filled with liquid of known of known density so if you wanna callibrate it just close block valve just before capilary @ high side & connect druck apply it's calibrated range pressure as normal calibration ensure low side block valve must be closed & if you asking commissioning so this is not a DP type pressure tx so simple if you wanna put in servie this tx just open high side block valve & than low side block same way i do it but still transmitter showing -13 ma.just tell me what i want to do ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)