one rtd sensor which is connected at middle of distillation
column where actual temp. is 100deg but when we tight this
sensor at thermowell end it goes down to 90 deg & when
remove from the thermowell(but sensor end dipped in well)
showing actual reading, what is reason?
Answers were Sorted based on User's Feedback
Answer / ashwin jain
when the RTD is loose, the RTD probe direct contact to
thermowell body so RTD giving the temp.(100 deg) but when
we tighten with thermowell there is sum gap or space
between thermowell body & probe,so temp down to 90 deg.
also check the OD of thermowell.
OD of thermowell > RTD
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / nitin
i want again clear my question that, rtd showing 100 deg temp. & it is ok, but as soon as i tight the length adjustment screw that is on rtd rod to the thermo well, temp. suddenly dropped down to 90 deg, what's reason
and again i untightened that screw and kept apart from thermo well, It again showing the correct reading. what's reason
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ashok
The Question is not clear bez always temperature needs time
to reach the actual value like 100deg. so when you take out
of it will not loose the temperature until we take the senor
out.
Is This Answer Correct ? | 1 Yes | 1 No |
Explain the difference between differial pressure & delta pressure?
How the flow can be measured by using DP Transmitter?
what is pyrometer? which purpose it has to be used?
can any one tell leakage class in control valve depend on which parameter and there is any specific table or chart for selection of valve leakage class
Induction type 1-p wattmeter reads ….. a) true value b) apparent value c)volt ampere value
3 Answers Engineers India Limited,
in any transimitter (flow/level) there are three terminals for supply& test (+,-,+)in two wire,24VDC given to Tx.,but how 4-20 ma signal travels thru same wire (as it is for 24VDC input supply)?
In Safe Guarding test what means by "Failed to Danger" ?
Where are oxygen analysers installed in cfbc boilers? What are their usual readings?
what r all the closed loop used in boiler? for this related tell some web address..
Difference b/w SCADA & DCS
how to calibrate level transmitter
how checking is done in fiber optic cable? explain the working of RTU?