explain why tap changer is always connected to high voltage
winding side of the transformer.
Answers were Sorted based on User's Feedback
Answer / inderpreet singh
There are many Advantages/reasons that the tap changer is connected to High voltage, some are described below:
1.HV winding is easy to Tap because HV winding is always placed on LV winding and LV winding is placed near to core due to insulation and cost constraints.
2. For keeping voltage at consumer end constant, Tap changer is provided on HV side.
3 In Electromagnetic field theory, Voltage & Current are inversely proportional to each other. where voltages are high currents will be low, when tap changer is connected to HV it will lead to avoid heavy inrush of current while tap changed.
Is This Answer Correct ? | 110 Yes | 5 No |
Answer / d4
The HV windings are placed on the LV windings, so it is easy
to take tappings from the HV side. Also the currrent in the
HV side is less than that on the LV side; this helps in
reducing the arcing which takes place as a result of tap
changing.
Is This Answer Correct ? | 35 Yes | 4 No |
Answer / zahid khan
tape changer is always connected to high voltage winding
side of the transformer to avoid heavy inrush current
Is This Answer Correct ? | 41 Yes | 16 No |
Answer / mithun
Actually a tap changer is used to get variable voltages. It
is just an air break switch. If it is connected in high
current side (LV side), there is more chances to occur
heavy sparks while in changing the taps, means while
changing the switch positions. In order to avoid that heavy
sparks in high current side, tapings are provided on low
current (HV side).
Is This Answer Correct ? | 19 Yes | 2 No |
Answer / k.rajmohan
The reason is current in HV is less than LV. The word
alway in question is not correct. The reason due
insulation problem some time tapchanger is plased in LV
side of the transformer.
Is This Answer Correct ? | 14 Yes | 8 No |
Answer / asad
It is difficult to tap the l.v winding since it is placed near to the core due to insulation consideration. it is easy to tap the h.v winding because it is outside the l.v winding, easily accessible and therefore can be tapped easily
Tap changers on the h.v side carry low current though more insulation have to be provided.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / vyankatesh badgujar
simply to avoid matter of rich current concern and it's always easy to provide tapping on outermost than innerone, as hv is outer winding.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / maurya kishan
High tension side me current ki Kumar kam hoti hai jisase tap changing gear ki size kam rakhani padati hai so.............
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / brajesh kumar chaudhary
Tapping ka main work voltage ko jarurat ke anusar voltage ko badhane ya ghatane ke liye hota hai. aur isko secondry side me lagate hai
Is This Answer Correct ? | 0 Yes | 3 No |
Answer / nidhi
to avoid high losses in case of not full load supply. when
smaller amount is required then it can be connected to that
Is This Answer Correct ? | 6 Yes | 20 No |
What will be advantage if we put some load in neutral of grounded star transformer & loadshortcircuit current,rated current of cable & MCB with example?
IS RTCC AND OLTC REQUIRED FOR 500 KVA 11KV/433V TRANSFORMER FOR AN INDUSTRY?
7 Answers IGCAR, TNEB Tamil Nadu Electricity Board,
what is the procedure for three phase motor differential relay testing can it do with single phase test kit?
findout of current?details 440v,3phase,085pf,hp-5
What is the diff btw Conventional & Addressable Fire Alarm System???
We have 2 11kv/433v transformers for 2saperate acb for mv panels and 1 bus coupler acb. Suppose I’ll close bus coupler what will happen or it will be share the load. Please suggestion and any modification required.
What is corona ? Mention its positve effects .
what is the diffrence between voltage and current?
how is the leakage current flow only through guard wire (when guard wire is connected in the circuit)????
what is the chemical reaction of solt and charcoal in earthing?
What is the "IS" for Rising Main?
HARMONICS ARE ALWAYS IN INTEGER LIKE 2ND OR 3RD HARMONICS,NOT IN FRACTION LIKE 0.5 HARMONICS.....????????