If we know the load for generator in KW then how it will be
change to amps and also if we know the load in amps how it
will change in KW and what Generator is good for
that...suppose load is 500 amps 3phase......??
Answer / ram t shelke
Techanically speaking , Generator is a DC machine i.e an
machine used to supply DC power.but you are saying that it
is a 3phase machine . so you might be talking about
alternator.
if you know the value of generator current , it can be
expressed in terms of KW provided one should know the
terminal or O/P voltage of generator.use following equation
for the required convertion.
KW = 3* TERMINAL VOLTAGE per phase (V) * RATED CURRENT
per phase (A) * power factor/1000
On the other hand , if you know KW out put, one can
calculate corresponding current by following equation
current per phase(A) = kw rating*1000/ 3* voltage per phase
(V)* power factor
| Is This Answer Correct ? | 0 Yes | 0 No |
To make a basic instrumentation amplifier, it takes A One op-amp with a certain feedback arrangement B Two op-amp and seven resistors C Three op-amps and seven capacitors D Three op-amps and seven resistors
What do you mean by passive circuit elements and why these are called passive?
Hello to all, Please someone can send me HPCL ELECTRICAL Engg. Sample papers to me? Its urjent....my email address is.... raviasiapacific@gmail.com
What is the difference between circuit and network.
15 Answers Jadavpur University, Sail, TCS,
how we have to calculate the short circuit current for 33/11kv 2mva, 7.5% Z, Transformer primary side breaker and secondary side breaker short circuit current for both sides?.
give some advantages and disadvantages of combiniing the session, presentation, and application layer in the osi model into one single application layer in the internet model
Tell the details of the precommissioning tests that are performed on distribution transformer, power cable and switchgear (11kv).
What kind of test is conducted commonly for generator? And explain briefly
the distance from my office to d.g is aprox 400mtrs and voltage drops ibn my office near about 40 volt what should i do p[ls suggest.
What is the effect of interchanging core(made of steel) and winding(made of copper) material in case of transformer? Give proper explanation in regard to different losses in transformer.
Why Generator rotate only clock wise ?
Can anyone explain how the vector diagram of a transformer which doesn't have name plate be found whether it is Dy11/Dy5/Yd11 and so on?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)