If we know the load for generator in KW then how it will be
change to amps and also if we know the load in amps how it
will change in KW and what Generator is good for
that...suppose load is 500 amps 3phase......??
Answer / ram t shelke
Techanically speaking , Generator is a DC machine i.e an
machine used to supply DC power.but you are saying that it
is a 3phase machine . so you might be talking about
alternator.
if you know the value of generator current , it can be
expressed in terms of KW provided one should know the
terminal or O/P voltage of generator.use following equation
for the required convertion.
KW = 3* TERMINAL VOLTAGE per phase (V) * RATED CURRENT
per phase (A) * power factor/1000
On the other hand , if you know KW out put, one can
calculate corresponding current by following equation
current per phase(A) = kw rating*1000/ 3* voltage per phase
(V)* power factor
Is This Answer Correct ? | 0 Yes | 0 No |
what is difference between vcb and mccb
how to select the rating of neutral ct with reference to transformer secondary current(in power transformer,stepdown tansformer,for example2000kva,11kv/415volt
In case of 3Phase Supply, Voltage R-Earth/Neutral - 220 Y-Earth/Neutral - 220 Z-Earth/Neutral - 220 Total is -> 660Volts Then Why it is said that 3Phase supply is 440
6 Answers Hindustan Unilever Limited,
How to resolve if Diesel generator stop while running ?
what is Use of Stones/Gravel in electrical Switch Yard??
how to check the LRS resistance .......................
What is the meaning of BREAKING and MAKING CAPACITY in case of CIRCUIT BREAKERS.
1 HP = how many Kva
If the kvar rating of capacitor bank is 600 kvar at 525V then what it's rating at 415v.
In MEP Services what are parts of STP and what are there function?
what mean by machin
Which type of power plant is more easier to produce electrical power at economical condition?