Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


I am getting differential earth fault in my transformer
realy , i have checked all its CT & control wiring but do
not get fault, Please help

Answers were Sorted based on User's Feedback



I am getting differential earth fault in my transformer realy , i have checked all its CT & co..

Answer / jiten sharma

Hi, some times when you charge the transformer after some
duration, trafo will take high inrush current. Due to that
it will trip on overcurrent but some times it can be also
give the triping on differential protection with
overcurrent.

So keep the setting slight high and then charge the
transformer. N after charging keep the setting as it is.

It might solve your problem but before that do the all test
on your trafo and then if nothing will found follow this.

Regards,
Jiten

Is This Answer Correct ?    3 Yes 0 No

I am getting differential earth fault in my transformer realy , i have checked all its CT & co..

Answer / arun

Do all the tests in the transformer windings then you will
get the fault.

Differential protection is given mainly to isolate the
circuit when there is fault inside the transformer.

Is This Answer Correct ?    2 Yes 1 No

I am getting differential earth fault in my transformer realy , i have checked all its CT & co..

Answer / vaidegi

yes

Is This Answer Correct ?    1 Yes 0 No

I am getting differential earth fault in my transformer realy , i have checked all its CT & co..

Answer / engineer

Check all your system(Incuding Cables and trandformer and
control circuit) From 1st CT (at HV Side)to 2nd CT at(LV
side).

Is This Answer Correct ?    1 Yes 0 No

I am getting differential earth fault in my transformer realy , i have checked all its CT & co..

Answer / k.prakashchandra

I think it is REFR which picks up only if there is earth
fault whithin the transformer .i.e. between LT an HT
CTs.and an NCT is to be provided

Is This Answer Correct ?    1 Yes 0 No

I am getting differential earth fault in my transformer realy , i have checked all its CT & co..

Answer / k.prakashchandra

Dif relay acts even for faults anywhere between cts .check
cable glands and all others between cts on primary and
secondary

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

whatis the difference between electrical and electronics?

11 Answers  


Two 11 kv lines are feeding to common bus in a substation,I have one set of CT & PT(3ct,2pt), How can I measure both lines power using single set.

6 Answers   L&T,


what is meant by MCB and MCCB? and what its full form?

7 Answers   Bajaj, JHM Hotels,


if field winding of synchronous generator are shorted on each other will it start or burn or run for short time like induction motor

1 Answers  


How the output,losses and temperature of machines varies with linear dimension?

1 Answers  


List out the types and name of the motor under their application?

0 Answers  


what's the requirement of Dy11d0 connection of 3 phase transformer?what's use of it?

0 Answers   Thermal Systems,


What is the difference between MCCB,ELCB,RCB & MCB

2 Answers   Bhel, HCL, HPL,


WHAT IS NORMAL VECTOR GROUP USED FOR DESIGNING OF TRANSFORMERS??

11 Answers  


HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CALCULATE CAPACITOR RANGE?

12 Answers   Al-Malik, All Star Electric, GEC, Reliance, Universal Industries,


why transformer core is eathed?

7 Answers   ECE,


in my observation NCT is used at Karnataka power transmission. why we are not used in andhra pradesh

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)