Two 11 kv lines are feeding to common bus in a
substation,I have one set of CT & PT(3ct,2pt), How can I
measure both lines power using single set.
Answers were Sorted based on User's Feedback
Answer / sb
Connect your CT & PT on the common bus to obtain combined
power of both the 11 kV lines.,
| Is This Answer Correct ? | 14 Yes | 5 No |
Answer / pradip
WHAT IS THE DIFFERENCE BETWEEN LINE PT AND BUS PT?
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / ravi prakash
nowadays dual energy meters are available.let the cts be on
the common bus.connect one set of pts on each 11 kv lines
.the energy meter has got two pt refernce terminals and it
will record the kwh of each line whenever power is
available.the make of meter is CADEL.
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / sreejith
connect 2 cts to any 2 phases and 1 pt to one of the 11 kv
line.this will give power by 2 wattmeter method. connect
one ct to any one phase of bus and connect one pt. From
this u can get power in bus as bus will be balanced and
total power will be 3 times one phase power. If u deduct
power in one 11kv line from power in bus u can get power
from 2nd 11kv line
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / raman jain
As 11 kV feeder is concerned , the load is more or less
balanced . So put one PT and one CT on R-Phase of each
line , and one can measure the power on bith feeders
approximate but not exactly.
| Is This Answer Correct ? | 1 Yes | 5 No |
What is the actual meaning of thermal power efficiency ?
show me the diagram of three phase wiring and also tell me hoe to take the readings of megger testing
Why inductor short on dc and capacitor allow to flow ac?
in cvt,there are two windings,1a,1n and 2a,2n.in my one project i use only one winding i.e.1a,1n. the other winding is not in use, so i connect it in open delta and want to close it by ibsertibg thermal resistor. the output of cvt is 132kv/115/sqrt3. plesae tell me exact value of resistor, so i may close it to avoid the resonance phenomenin. send me answer on this email adress please. aetcon-po@aetcon.com
how to give earthing in plain?
Why Nutral CT rating for Earth Fault Protection of Transformer neutral shall be 20% of Full load Current of Transformer
I am having a DG set.The 415 V from Generator is step up to 460 v and then the same is used for Induction furnace. before Step up, I am connecting LT load to my factory use. When Induction furnace is in service from DG, when i try to start a motor, the generator is tripped.Please tell me the reason.
why we have and use 3 phase not 2 or 4 or other in power system?
what are the changes made in induction motor so that it act as induction generator
how electronic energy meter works?
Define non-touching loop.
why in transformer there is not rotating fiddl/ magnetic field like motor
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)