Two 11 kv lines are feeding to common bus in a
substation,I have one set of CT & PT(3ct,2pt), How can I
measure both lines power using single set.
Answers were Sorted based on User's Feedback
Answer / sb
Connect your CT & PT on the common bus to obtain combined
power of both the 11 kV lines.,
| Is This Answer Correct ? | 14 Yes | 5 No |
Answer / pradip
WHAT IS THE DIFFERENCE BETWEEN LINE PT AND BUS PT?
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / ravi prakash
nowadays dual energy meters are available.let the cts be on
the common bus.connect one set of pts on each 11 kv lines
.the energy meter has got two pt refernce terminals and it
will record the kwh of each line whenever power is
available.the make of meter is CADEL.
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / sreejith
connect 2 cts to any 2 phases and 1 pt to one of the 11 kv
line.this will give power by 2 wattmeter method. connect
one ct to any one phase of bus and connect one pt. From
this u can get power in bus as bus will be balanced and
total power will be 3 times one phase power. If u deduct
power in one 11kv line from power in bus u can get power
from 2nd 11kv line
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / raman jain
As 11 kV feeder is concerned , the load is more or less
balanced . So put one PT and one CT on R-Phase of each
line , and one can measure the power on bith feeders
approximate but not exactly.
| Is This Answer Correct ? | 1 Yes | 5 No |
HOW TO IDENTIFY THE RELAYS WHICH APPLICATION IN WHICH RELAY USING
why transformer rating in kva ?
WE are using a 63A MCCB(SIEMENS MAKE) for one of the feeder in LV substation panel.It is supplying to a lighting & power socket DB.Settings in the MCCB is Ir = 63 * 1 , Isd = 8 times of Ir , tsd = 0.5 sec( I2 t off). Sometimes this MCCB is tripping .But no trip in DB MCB. Can anybody tell me reason ? From where i can know about the MCCB settings?
there is a power transformer 66/11kV in delta-delta connection has 5 feeder coming out from the secondary side. One of the feeder in it normally loaded (loaded than other feeder)and this feeder usually trips with double OCR causing the bank transformer to trip. Now if the load of this feeder is put on other transformer then that no problems occurs on that transformer or the load. However normally all the test(IR, PI, short ckt, open ckt,grounding test and other ) has been conducted for this but evertything transformer..... I am not geting what is the actual problem...
AP Transco Assistant Engineer (Electrical) Model Question papers
2 Answers APTransco, HCL, Tranco, UPSC, VMware,
plz send me the procedure and syllabus for mseb exam
how to calculate the over current rating of 3phase motor
what are the ''pitting rings''and how cn they be controlled in a series generator
Hi friends, i m electrical engineer i want a cdr for migration purpose so anybody have information about this then send me on jayesh_ee88@yahoo.com.please try to me
What is the importance of creepage distance in disc insulator ?
What is the type of earth fault protection used in battery? explain.
how to calculate the torque of a motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)