Two 11 kv lines are feeding to common bus in a
substation,I have one set of CT & PT(3ct,2pt), How can I
measure both lines power using single set.
Answers were Sorted based on User's Feedback
Answer / sb
Connect your CT & PT on the common bus to obtain combined
power of both the 11 kV lines.,
Is This Answer Correct ? | 14 Yes | 5 No |
Answer / pradip
WHAT IS THE DIFFERENCE BETWEEN LINE PT AND BUS PT?
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / ravi prakash
nowadays dual energy meters are available.let the cts be on
the common bus.connect one set of pts on each 11 kv lines
.the energy meter has got two pt refernce terminals and it
will record the kwh of each line whenever power is
available.the make of meter is CADEL.
Is This Answer Correct ? | 2 Yes | 5 No |
Answer / sreejith
connect 2 cts to any 2 phases and 1 pt to one of the 11 kv
line.this will give power by 2 wattmeter method. connect
one ct to any one phase of bus and connect one pt. From
this u can get power in bus as bus will be balanced and
total power will be 3 times one phase power. If u deduct
power in one 11kv line from power in bus u can get power
from 2nd 11kv line
Is This Answer Correct ? | 0 Yes | 3 No |
Answer / raman jain
As 11 kV feeder is concerned , the load is more or less
balanced . So put one PT and one CT on R-Phase of each
line , and one can measure the power on bith feeders
approximate but not exactly.
Is This Answer Correct ? | 1 Yes | 5 No |
How many earthings are required for commissioning the Transformer?
WHAT IS FAULT CAPACITY OF HT MOTOR TERMINAL BLOCK? ANY BODY HAVE ANSWER PLZ....POST IT.
Usage of flywheel diode in relays
while starting a liquid starter ,is there any volage drop on water/soda on tank.can we touch the tank on starting?
Which type of drive is advantageous AC or DC and why?
1kva = kw ?
Write the analogous electrical elements in force voltage analogy for the elements of mechanical translational system.
what is the k var ratting of 1250kva
What is ht lt switchgear.
3 Answers Bhel, HBL Power Systems,
why circuit breaker closing time is always higher then tripping / opening time.
How to findout raw or ups power? its not indicated in socket,
if we put a energy meter in 500 kvar capacitor bank ,then how much units show in energy meter per day.