Why only negative 24 vdc supply give in vibration measuring
system.
Answers were Sorted based on User's Feedback
Answer / nandan
The principle is that analyzer supplies a negative voltage
to transducer,who converts it into a frequency & sends it
across the probe.Now as the probe comes into the area of
rotor it creates a magnetic field & with it eddy current is
produced on the rotor side.Which changes the amplitude of
the frequency.It induces the voltage & remaining frequency
comes to the transducer through the return way.Transducer
converts it into the voltage .
Now coming back to the question The gap voltage has a
negative relation with the voltage induced i.e. as the gap
increases the induced voltage decreases.So to make it to
into a linear relation ship, negative voltage is supplied.
i.e
Gap Gap voltage
0 mm 0 vtg
1 mm -9 voltage
2 mm 18 voltage
& when the probe is in air it will have no induced voltage
so all -24 voltage without induced voltage will return back.
Is This Answer Correct ? | 16 Yes | 7 No |
Answer / jigaranadkat
Because it has PNP transistor inside which requires base
bias of negative (-ve) supply.
Is This Answer Correct ? | 11 Yes | 4 No |
Answer / darpan
The principle is that analyzer supplies a negative voltage
to transducer,who converts it into a frequency & sends it
across the probe.Now as the probe comes into the area of
rotor it creates a magnetic field & with it eddy current is
produced on the rotor side.Which changes the amplitude of
the frequency.It induces the voltage & remaining frequency
comes to the transducer through the return way.Transducer
converts it into the voltage .
Now coming back to the question The gap voltage has a
negative relation with the voltage induced i.e. as the gap
increases the induced voltage decreases.So to make it to
into a linear relation ship, negative voltage is supplied.
i.e
Gap Gap voltage
0 mm 0 vtg
1 mm -9 voltage
2 mm 18 voltage
& when the probe is in air it will have no induced voltage
so all -24 voltage without induced voltage will return bac
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mohammed abbas
Because it is NPN tansistor during the initail days when
this was inveted by bently the cost of NPN transiator was
less. then they started use NPN transiator for the
vibration propbe, due to this we will give negative 24vdc
supply
Is This Answer Correct ? | 5 Yes | 7 No |
Answer / sai kiran.c
does really negative voltage exists......???
Is This Answer Correct ? | 0 Yes | 5 No |
Yokogawa mass flow meter shows negative reading...what r the main causes for this problem?...
how to convert MA in to measuring values..and how mwasuring values into MA ?..plz ansr.i have intervw
if change the pid in D value so what action.
How ejector(or)evactor air pump is working in thermal power plant?
Explain how thw analog to digital converter works with the circuit diagram
What is difference between converter & transducers?
what sud u do if u dont get feedback from control valve?
which is the best type to measure level of a Tank(water). Displacer or Differential Pressure method?
what is the procedure of O2 analyser calibration?
procedure to commission a drum level transmitter
TEMPERATURE VARIATION FOR FREQUENTLY.
HELLO FRENDS ,, I M IN THE MIDST OF TROUBLE .. JUST LITTLE HELP ME... SUPPOSE ,, I HAVE A CLOSE VESSELE TANK ( HEXANE MEDIA ) ,, I M USING ROSEMOUNT 2051 DPT FOR LEVEL APPLICATION .. ITS CALIBRATE RANGE IS.. . 0 TO 950 MMH20 ..I DID CALIBRATED DPT WITHOUT REMOVING IMPULSE LINE OF HIGH AND LOW TAPPING.. & WITHOUT DISTURB 3 WAY MANIFOLD..!!! BUT ,,, DURING CALIBRATION I SELECT RANGE BY HART LRV IS 900 MMH20 & URV IS 1300 MMH20 ,, BUT ,TANK LEVEL SOMETIMES 100 % AT 1100 MMH20 , SOMETIMES 1300 MMH20 ..IN THIS CONDITION .. WHOLE LOOP FAILED ,, MAIN THING IS THAT ,, HOW TO CUSTOME RANGE SELECT ?? AND IF I USED RANGE OVER THE ORIGINAL CALIBRATE RANGE ,,,THEN WHAT ERROR WILL BE COME ??? HOW TO ZERO CALIBRATION OF DPT... HOW TO ZERO TRIM BY MANIFOLD ?? AND FOR TANK LEVEL PURPOSE ... WHICH UNIT I CAN USE ??? IS THERE ANY CALCULATION OR CALIBRATION .. IF YEH .. THEN PLZ JUST GIVE ME CALIBRATION STEPS FOR DPT.. THANKS YOURSSSSSSS