why r using 250 resistances
Answers were Sorted based on User's Feedback
Answer / ayaz
250 ohm use in loop only for hart protocol and use only smart devices
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / ashraf
According to the HART Foundation spec, the 1200-2400 Hz HART signal needs a minimum (230 ohm) resistance in the loop to create a HART signal with enough amplitude to meet the sensitivity requirements of a HART modem receiver.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / hitesh
convert analog signal 4-20mA to digital signal 1-5V
| Is This Answer Correct ? | 0 Yes | 0 No |
The power supply is a low impedance to the hart signal
shorting it out. Adding the resistor raises the impedance
so that the signal can be detected by the calibrator. The
HART protocol uses 1200 baud Frequency Shift Keying (FSK)
based on the Bell 202 standard to superimpose digital
information on the conventional 4 to 2OmA analog signal.
Nilesh Bhagwat ( Sr. Inst Tech)
| Is This Answer Correct ? | 2 Yes | 4 No |
what is the difference in Kg/cm2 and mmwc?
What is DDC-MIS?
what is difference between pressure,flow and level control valve.
find the kp ki kd from the transper function G(S)=29.44s+04707/1.5349s2+s
how to given power supply of any type two wire transmitter in field?
Is there devices to convert mechanical energy/rotational energy into electrical energy.......? PLease suggest me....
if my 6 kva UPS gives 20 min. backup at 100 % load, then at 25% load what is the backup time?
PID controller is used for which type of compensation…… a) lead comp. b) lag com. c) lead lag com.
12 Answers Engineers India Limited,
where Pirani gauges are uesd in case of pressure measurement?
In split range control, we will control 2 outputs with time interval. Eg :(with 4-20 ma signal, for 4-12 ma we are operating one control instrument like valve & for 12-20ma we are operating other control instrumet (other valve). If we get a signal of 15ma to first instrument (Valve 1), what will happened to the first valve, and if we get signal above 20 ma to 2 valve what will happened ?
Why DP level transmitter preferred for closed vessels and Radar level transmitter for open tanks??
what is difference between E/P positioner and I/P positioner. Why E/P fixed in below actuator and why I/P fixed in other place
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)