can we control operation of PLC from operator station?
Answers were Sorted based on User's Feedback
Answer / nilesh
Question not clear.
1.PLC has its own controller which execute the
program.Before every program run PLC read the input and
after program execution generate output accordingly.
2.If PLC I/O need to be control from operator station (
DCS/SCADA) then PLC need to be connected to OS through
serial link/Ethernet
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / ashish namdev
Operation station system no have any program (programming built in Engg. Station Only which is a server also)
but operating station system is connected with same network of plc/Dcs through Ethernet or other.
than that station has a SCADA software which is connect it to server system station through IP protocol.
than we can access or give command through Operating station.
Ashish Nmadev
Sr. Engg In Jaypee thermal power plant, Bina(MP)
Is This Answer Correct ? | 0 Yes | 0 No |
Pressure transmitter working Principles?
for what purpose strain guage is used?
What are de-saturators?
What care will you take in the installation of control valves,SCADA,DCS and FOC in Oil and Gas Project?
what is zenier barier and what means zone 1,zone 2,and zone 3
2 Answers Bapco Bahrain Petroleum Company,
To find closed tank level by DP transmitter , how to findout its range.and insomeplace they using range like - 1500 to +1500 mmwc why not 0 to 3000 mmwc. how they spilit they range for minus and plus.and why?
which transister (npn or pnp) is used in vibration monitoring for negative voltage?
What is 3 element control system
What is the detail function of I/O card in DCS ? Why we dont use the I/O directly with controller?
What is the use of temprature compensation?
How can we say that accuracy of measurement increases by using 3 or 4 wire RTD? because for example: If resistance of RTD element is say r ohms and Resistance of the cable from transmitter to RTD is R ohms And if 4 wire RTD is used, ____._____________________ R ohms | |_____._____________________ R ohms / \ / r ohms \ \ | |______.__________________ R Ohms | |_______._________________ R ohms Then the actual resistance measured will be: Total = r + R/2 + R/2 = r +R Ohms Note: r+R instead of r ohms. hence error
What are the materials use for COntrol Valve body?
1 Answers KNPC, Qatar Petroleums,