Range is Negative mmWC to Zero because we are using "Wet leg configuration" arrangement. In which LP side of transmitter is contains a Condesate Pot always filled-in with water.
Wet leg configuration is used when the tanks contain CONDENSABLE VAPOURS, these vapours when entered impulse lines may be condensed over time and get accumulated. This accumulated liquids in impulse line creates Pressure head resulting error in level measurement. to avoid this suituation we initially fill LP side impulse line with water ( or a condensate pot is used to condense vapour and fill impulse line automatically).
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / mithilesh kumar
actually wht happen there..
level is totally depend upon vessel/drum/tank type..
means that it is open or close..
if it's open then range is in positve..
but if it's fully closed then range is start with negative..
by using level formula..
u can mail me if this formula or step is required..
email id: mithilesh.barnwal30@gmail.com
| Is This Answer Correct ? | 5 Yes | 18 No |
In both cases you are using a wet leg configuration with the
DPT. In the steam drum if you use the old fashion way by
changing the HP and LP legs around you will get a positive
mmH2O reading. If you use a piped SMART Tx or a SMART
capillary type DPT, you will get this negative mmH2O readings.
I have already done a writeup on this so go and look at
previous questions.
In the deaerator there is a vacuum but again the same wet
leg is done. I have already done a writeup on this vacuum
applications as well so go and look at previous questions.
Good luck
| Is This Answer Correct ? | 7 Yes | 30 No |
when we calibrate the DP transmitter at that time which matrial we used in pressure pump?
Make a ladder diagram on LSL valve will close, on PSL valve will open and start the motor
Why is a dead weight tester so called by that name?
What is wet leg condition and why is it used?
Please explain about FAT? What is the difference between FAT and SAT?
Explain an adaptive / self-tuning controller’s major draw card.
Whether the DI, DOs shields can be connected with Analog Input Shield Earthpit?
what is stability
what is the meaning of HART ?
In split range control, we will control 2 outputs with time interval. Eg :(with 4-20 ma signal, for 4-12 ma we are operating one control instrument like valve & for 12-20ma we are operating other control instrumet (other valve). If we get a signal of 15ma to first instrument (Valve 1), what will happened to the first valve, and if we get signal above 20 ma to 2 valve what will happened ?
1)how we calculate the drum level? and how we select the transmitter range?
CONTROL VALVE OPERATING IN MANUAL BUT NOT IN MANUAL. WHAT SHOULD BE THE PROBLEM ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)