why the steam drum and deaerator level transmitter range is
in negative MMWC to zero
Answers were Sorted based on User's Feedback
Range is Negative mmWC to Zero because we are using "Wet leg configuration" arrangement. In which LP side of transmitter is contains a Condesate Pot always filled-in with water.
Wet leg configuration is used when the tanks contain CONDENSABLE VAPOURS, these vapours when entered impulse lines may be condensed over time and get accumulated. This accumulated liquids in impulse line creates Pressure head resulting error in level measurement. to avoid this suituation we initially fill LP side impulse line with water ( or a condensate pot is used to condense vapour and fill impulse line automatically).
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / mithilesh kumar
actually wht happen there..
level is totally depend upon vessel/drum/tank type..
means that it is open or close..
if it's open then range is in positve..
but if it's fully closed then range is start with negative..
by using level formula..
u can mail me if this formula or step is required..
email id: mithilesh.barnwal30@gmail.com
| Is This Answer Correct ? | 5 Yes | 18 No |
In both cases you are using a wet leg configuration with the
DPT. In the steam drum if you use the old fashion way by
changing the HP and LP legs around you will get a positive
mmH2O reading. If you use a piped SMART Tx or a SMART
capillary type DPT, you will get this negative mmH2O readings.
I have already done a writeup on this so go and look at
previous questions.
In the deaerator there is a vacuum but again the same wet
leg is done. I have already done a writeup on this vacuum
applications as well so go and look at previous questions.
Good luck
| Is This Answer Correct ? | 7 Yes | 30 No |
How to Calibrate Ultrasonic flow Transmitter in Field
I have got a call of IOCL interview for projects having 2yrs experience. What sort of questions should I expect in the interview?
What is use of condensate pot
5 Answers Alstom, Petrocil, Samsung,
what is wave length were using ?
Instrumentation symbols interpration, P& ID, Logic diagram analysis, Electrical drawing analysis.
what is the PID controller?
What is the different between of rtd and thermocouple ?
what is the field bus calble ? what are diffrences in orang colur cable and black coular calble ?
How to Calibrate Level Troll in field
why are use only 4 to 20ma. signal.
what is intrument termination what is commisioning
Calibration procedure for water rotameters
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)