Answer / umesh kumar
As we know that 1 KW = 3413 btu ( British thermal unit)
and 1 TR = 12000 btu
kw capacity = 12000/3413
Hence 1 TR = 3.5 kW
| Is This Answer Correct ? | 239 Yes | 45 No |
Answer / khaleel
Lets say
Chiller Capacity 100TR
Power Consumption 70KW
Then IKW/TR = 70/100 = 0.70 KW/TR
| Is This Answer Correct ? | 210 Yes | 22 No |
Answer / r.gandhi
1 KW = 3413BTU
1TR = 12000 BTU
KW=12000/3412
1TR= 3.5KW
| Is This Answer Correct ? | 120 Yes | 26 No |
Answer / tapan abdul kalam
As we know that 1 KW = 3413 btu ( British thermal unit)
and 1 TR = 12000 btu
kw capacity = 12000/3413
Hence 1 TR = 3.5 kW
| Is This Answer Correct ? | 66 Yes | 12 No |
Answer / vivek namdeo
IKW/TR = consume power in k.w./generated chiller TR
| Is This Answer Correct ? | 59 Yes | 8 No |
Answer / palash bolia
1 Ton of Ice = 2000 Pounds(909.1 Kg)
Latent Heat of Ice = 335 kJ/kg
Amount of Heat removed to form 1 ton of (british) ice from
0deg of water to 0deg ice =
(909.1 X 335)/(24 X 3600) = 3.5 KW
| Is This Answer Correct ? | 34 Yes | 3 No |
Answer / sumesh
Here comes the importance of COP which is always greater than 1
Both the answers are correct.
1 Ton = 3.5 kw
but for producing 1tr,only .7-.9 kw/tr(depending on machine).
for more clarification read and understand "coefficient of perfomance"
| Is This Answer Correct ? | 36 Yes | 6 No |
Answer / gaurav majumdar
Basically HVAC Engg know 1 kilocalorie (kcal)= 3.97 Btu
So 1 TR = 3.52 KW
| Is This Answer Correct ? | 32 Yes | 5 No |
Answer / kuna
KW = 3413BTU
1TR = 12000 BTU
KW=12000/3412
1TR= 3.5KW
| Is This Answer Correct ? | 19 Yes | 4 No |
How may I get the maximum current capacity for a particullar size Alluminum or Copper cable if there is compulsion to use?
How to determine alternating current frequency?
how to calculate percentage impedence at 75 deg C at normal tap
what is the difference between watts and volts?
Why annealing is done on transformer core manufacturing process?
As i want some model question paper in basic computer science and history please send me immediately sir
0 Answers TNPSC Tamil Nadu Public Service Commission,
I want formula to calculate current loss with distance in km.I searched many sites but didn't right answer.Plz reply me
why name plate detail HP/KW rating of a motor is different from measured value HP/KW using formula?
what id a dry type transformers and its function ?
what is the difference between thermal magnetic release and microprocessor based release breakers. what are the advantages of latter over the first one...
5 Answers Jackson, Karthik Industries, McD BERL, TCS,
In an panel board if the outgoings are power plugs and motor equipments...what should we choose as the incomer of the of the panel board?? MCCB OR ISOLATOR?? Should we use ELCB protection??if so where??
1. what is usage for power factor in industries?? 2.why we need to monitor power factor??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)