how do you calculate IKW(consumption per TR) in HVAC?
Answers were Sorted based on User's Feedback
Answer / umesh kumar
As we know that 1 KW = 3413 btu ( British thermal unit)
and 1 TR = 12000 btu
kw capacity = 12000/3413
Hence 1 TR = 3.5 kW
| Is This Answer Correct ? | 239 Yes | 45 No |
Answer / khaleel
Lets say
Chiller Capacity 100TR
Power Consumption 70KW
Then IKW/TR = 70/100 = 0.70 KW/TR
| Is This Answer Correct ? | 210 Yes | 22 No |
Answer / r.gandhi
1 KW = 3413BTU
1TR = 12000 BTU
KW=12000/3412
1TR= 3.5KW
| Is This Answer Correct ? | 120 Yes | 26 No |
Answer / tapan abdul kalam
As we know that 1 KW = 3413 btu ( British thermal unit)
and 1 TR = 12000 btu
kw capacity = 12000/3413
Hence 1 TR = 3.5 kW
| Is This Answer Correct ? | 66 Yes | 12 No |
Answer / vivek namdeo
IKW/TR = consume power in k.w./generated chiller TR
| Is This Answer Correct ? | 59 Yes | 8 No |
Answer / palash bolia
1 Ton of Ice = 2000 Pounds(909.1 Kg)
Latent Heat of Ice = 335 kJ/kg
Amount of Heat removed to form 1 ton of (british) ice from
0deg of water to 0deg ice =
(909.1 X 335)/(24 X 3600) = 3.5 KW
| Is This Answer Correct ? | 34 Yes | 3 No |
Answer / sumesh
Here comes the importance of COP which is always greater than 1
Both the answers are correct.
1 Ton = 3.5 kw
but for producing 1tr,only .7-.9 kw/tr(depending on machine).
for more clarification read and understand "coefficient of perfomance"
| Is This Answer Correct ? | 36 Yes | 6 No |
Answer / gaurav majumdar
Basically HVAC Engg know 1 kilocalorie (kcal)= 3.97 Btu
So 1 TR = 3.52 KW
| Is This Answer Correct ? | 32 Yes | 5 No |
Answer / kuna
KW = 3413BTU
1TR = 12000 BTU
KW=12000/3412
1TR= 3.5KW
| Is This Answer Correct ? | 19 Yes | 4 No |
what is meant by earth fault and how it happens....
How we detect the leakage current of 11 KV H.T. motors and waht is the maximim limit?
while running ,synchronous generator is being turned off.what will happen to the current flow??
kindly send me 11KV MV motor differential protection procedure by primary injection method.
How to select a transformer group to connect a 0,433 KV generation with 33 KV grid in bi directional flow of current
Hi,iam a diploma in electrical engineering.rtd from indian air force in apr 2007.prsently working in reliance next link as a network maintenance engineer since 2007,can i get a job in motherson sumi.
0 Answers Motherson, Motherson Molds and Diecasting Ltd.,
How to calculate the 2500 Kva Transformer losses Primary 11KV Secondary 415volts
1.dg on load alarm/stop alarm... 2.dg on load. piu alarm alarm kaise chek krte hai
How Calculat the Cable Sizing of HT/LT System & Explian by one Exampal?
HOW MANY POLES ARE THERE IN 3 SLOTS PER POLE PER PHASE MOTOR
what is submersible pump?what is different between motor and sub motor?
check list of maintenance of transformer?
11 Answers ABC, Cosmos, EPRON, Essar, Godrej, Hescom, Infosys, KPTCL, TCS,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)