how do you calculate IKW(consumption per TR) in HVAC?
Answers were Sorted based on User's Feedback
Answer / umesh kumar
As we know that 1 KW = 3413 btu ( British thermal unit)
and 1 TR = 12000 btu
kw capacity = 12000/3413
Hence 1 TR = 3.5 kW
| Is This Answer Correct ? | 239 Yes | 45 No |
Answer / khaleel
Lets say
Chiller Capacity 100TR
Power Consumption 70KW
Then IKW/TR = 70/100 = 0.70 KW/TR
| Is This Answer Correct ? | 210 Yes | 22 No |
Answer / r.gandhi
1 KW = 3413BTU
1TR = 12000 BTU
KW=12000/3412
1TR= 3.5KW
| Is This Answer Correct ? | 120 Yes | 26 No |
Answer / tapan abdul kalam
As we know that 1 KW = 3413 btu ( British thermal unit)
and 1 TR = 12000 btu
kw capacity = 12000/3413
Hence 1 TR = 3.5 kW
| Is This Answer Correct ? | 66 Yes | 12 No |
Answer / vivek namdeo
IKW/TR = consume power in k.w./generated chiller TR
| Is This Answer Correct ? | 59 Yes | 8 No |
Answer / palash bolia
1 Ton of Ice = 2000 Pounds(909.1 Kg)
Latent Heat of Ice = 335 kJ/kg
Amount of Heat removed to form 1 ton of (british) ice from
0deg of water to 0deg ice =
(909.1 X 335)/(24 X 3600) = 3.5 KW
| Is This Answer Correct ? | 34 Yes | 3 No |
Answer / sumesh
Here comes the importance of COP which is always greater than 1
Both the answers are correct.
1 Ton = 3.5 kw
but for producing 1tr,only .7-.9 kw/tr(depending on machine).
for more clarification read and understand "coefficient of perfomance"
| Is This Answer Correct ? | 36 Yes | 6 No |
Answer / gaurav majumdar
Basically HVAC Engg know 1 kilocalorie (kcal)= 3.97 Btu
So 1 TR = 3.52 KW
| Is This Answer Correct ? | 32 Yes | 5 No |
Answer / kuna
KW = 3413BTU
1TR = 12000 BTU
KW=12000/3412
1TR= 3.5KW
| Is This Answer Correct ? | 19 Yes | 4 No |
why after termination of HT cable armoured earth connected one end, why not connect other end.pls tell me correct answer.
in alternator why on load terminal voltage is less than no load teprminal voltage
why do we require two lines one phase and a neutral for an ac transmission..is neutral potential zero..?if yes y carry a neutral line from generating station itself...why dont we take it from ground
why the neutral point is zero in star connection?
What will happen if apply dc source for power transformer
why mostly conductor made by 7 nos wire?
in conventional fan regulators how the current varies with speed?
Why is making current of CB always greater than CB breaking burrent?.
what happen to the voltage and current in all phases when an earth fault occur in a phase in three phase three wire system(delta connected)...
ANY ONE TELL ME ABOUT generator synchronization panel panel to synchronise 3 gen of 250kva both automatic and manual. 2 gen output vol 415 3ph, 1 gen output vol 400 3ph SEND THE DETAILS DIAGRAM ON THIS EMAIL ADDRESS ayazleo@hotmail.com as soon as possilble best ragrds electrical engineer ayaz mahmood SAUDI TECH
we done magnetic balance test for 33KV /440V transformer in our company , but the ratio out is confusing us Voltage applied in RY = 440 , at RB = 320 and YB = 60 RY 440 = ( RB + YB ) 380 only Please let me know what type of problem is it.
What is the real function of reverse power relay in generator panel while syncronising?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)