Answer / umesh kumar
As we know that 1 KW = 3413 btu ( British thermal unit)
and 1 TR = 12000 btu
kw capacity = 12000/3413
Hence 1 TR = 3.5 kW
| Is This Answer Correct ? | 239 Yes | 45 No |
Answer / khaleel
Lets say
Chiller Capacity 100TR
Power Consumption 70KW
Then IKW/TR = 70/100 = 0.70 KW/TR
| Is This Answer Correct ? | 210 Yes | 22 No |
Answer / r.gandhi
1 KW = 3413BTU
1TR = 12000 BTU
KW=12000/3412
1TR= 3.5KW
| Is This Answer Correct ? | 120 Yes | 26 No |
Answer / tapan abdul kalam
As we know that 1 KW = 3413 btu ( British thermal unit)
and 1 TR = 12000 btu
kw capacity = 12000/3413
Hence 1 TR = 3.5 kW
| Is This Answer Correct ? | 66 Yes | 12 No |
Answer / vivek namdeo
IKW/TR = consume power in k.w./generated chiller TR
| Is This Answer Correct ? | 59 Yes | 8 No |
Answer / palash bolia
1 Ton of Ice = 2000 Pounds(909.1 Kg)
Latent Heat of Ice = 335 kJ/kg
Amount of Heat removed to form 1 ton of (british) ice from
0deg of water to 0deg ice =
(909.1 X 335)/(24 X 3600) = 3.5 KW
| Is This Answer Correct ? | 34 Yes | 3 No |
Answer / sumesh
Here comes the importance of COP which is always greater than 1
Both the answers are correct.
1 Ton = 3.5 kw
but for producing 1tr,only .7-.9 kw/tr(depending on machine).
for more clarification read and understand "coefficient of perfomance"
| Is This Answer Correct ? | 36 Yes | 6 No |
Answer / gaurav majumdar
Basically HVAC Engg know 1 kilocalorie (kcal)= 3.97 Btu
So 1 TR = 3.52 KW
| Is This Answer Correct ? | 32 Yes | 5 No |
Answer / kuna
KW = 3413BTU
1TR = 12000 BTU
KW=12000/3412
1TR= 3.5KW
| Is This Answer Correct ? | 19 Yes | 4 No |
tube light how its working.,?
How is the AVR working?
what is meant by class 1 E in electrical power supply?
how many ampere Maxmium load given on a 10 kva DG set?
hi frnds what is meant by harmonics & what is meant by third hormonics,where its will occur ?thank u
In EHV tranm. The conductors are …….. a) Cu roads b) Cu bars with Si c) Cu tube with Si plate
2 Answers Engineers India Limited,
prove that power consumed in 3 phase delta system is 3 times as compared to 3 phase star system
what is the excess air in furnace
which of the following elements is not present in stainless steel
the winding of Generator and Motor is star or in delta ? and why
What is the difference between Floot charge and Trickle Charge.
A powerplant has 8 gensets operating in grid parallel mode. In one genset sometimes there is pf variation and kvar variation. The plant operates in pf mode. When this variation is observed the load is stable, voltage is also stable, freq and genset speed is also stable. How will you check the functioning of pf card. What shall be the ideal output vdc of the pfc, from there it is input to AVR?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)