how do you calculate IKW(consumption per TR) in HVAC?
Answers were Sorted based on User's Feedback
Answer / shubhabrata sengupta
Chiller IKW/TR
Chiller Rating - 650 TR
Power Consumption – 100 KW
IKW/TR = Consumed Power in KW / Generated chiller TR.
Chiller is running at 34% i.e. 221 Generated chiller TR
Therefore IKW/TR is 100/221 = 0.45
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / balram singh mnadloi
TR= (delta T*flow)/(3.5*0.86)
and
KW=(1.73*V*I*PF)/1000
Then you have to divide TR by KW so you find Ikw of chiller
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / shashi
Halo guyz,1TR =3.5KW is not electrical power .it is thermal unit .So don't confuse
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ashok
1TR --- 3.5KW
1kw ----8633btu
1TR -----12000BTU
1kw/TR --- 1.396
| Is This Answer Correct ? | 24 Yes | 26 No |
Answer / puneet prashar
As we know that 1 KWh = 3413 btu ( British thermal
unit)But not 1kw, but it is = 8633 btu
and 1 TR = 12000 btu
kw capacity = 12000/8633
Hence 1 TR = 1.39 kW
| Is This Answer Correct ? | 6 Yes | 14 No |
Answer / jitendra patel
IKW in HVAC = (Chilled water TR x 3025)/860
for example Hvac = 200Tr
Ikw = 200*3025/860
=703.48
| Is This Answer Correct ? | 17 Yes | 29 No |
Pure inductive ckt takes power from AC when 1. Applied voltage and Current increases 2. applied voltage and current decreses 3. voltage decreases and current decreases please justify
-How do you select cable size for a given load at a given distance from source of supply. How do you find voltage drop.
Why the efficiency of a three-phase induction is the motor is less than that of a three-phase transformer?
Upto what extent, the lagging power factor can be improved with the help of capacitors?
why we dont store the ac power in battery?
What are linear elements and non linear elements? and I don't want answers with graph related
what is the transformer turn ratio formula and give some examples?
can any one tell me the formula to select the thickness of wire selection according to ampere rating
why the genearation of electricity always in form of sine wave only ??? why not cosine wave ???
Please send specifications for 1000KVA dry type transformer or where I can get the specifications?
X/R ratio in 11kv transmission line is?
What is the main feature of v/f control?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)