A 200 KVA UPS's load current is 70 A. We want to provide a
Generator back up. What capacity of DG required for this ?
Answer / laxmikant
Question is not clear,
Because 200kVA/(1.732x0.415kv)= 278.24 Amps/phase.
Please check. If you load demmand is 200kVA , as DG runs
always with 89% efficiency @ 100% load, You may choose for
250kVA DG.
| Is This Answer Correct ? | 2 Yes | 0 No |
Why distribution transformer secondary voltage is 0.433kV instead of 0.415kV.all other switchgear rating are 415 volt??
What's ND relay & it's functions?
hi i am aziz electrical associate engineer. i am faceing problem in acs800 vvvf drive.it is tripping wothout any alarm/fault.i cheaked all parameters and fault function of drive, all are correct as well as communication parameters.but still it is tripping (drive is tripping in running position not in starting)
how am i achived model paper to prepratio for bhel exam
What is GIS (Gas Insulated Switchgear)
when we connect a ceiling fan to a inverter's output voltage, it give some noise, why?
in my observation NCT is used at Karnataka power transmission. why we are not used in andhra pradesh
what happen when generator neutral supply and transformer neutral supply linked
why we store only dc in batteries ?
How to calculate HV Cable Sizing & what are the factors to be considered for selection?.
What is the acceptance value of leakage current in HI POT test
why capacitance effect is predominant in underground cable transmission and inductance effect is predominant in over head line transmission?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)