how do you calculate IKW(consumption per TR) in HVAC?

Answers were Sorted based on User's Feedback



how do you calculate IKW(consumption per TR) in HVAC?..

Answer / nilantha warushavithana

1 TR = 12,000 BTU/h
1 BTU/sec = 1.055 kW
12,000 Btu/h = 3.5166 kW
1 kW = 3412.3 BTU/h

Is This Answer Correct ?    14 Yes 1 No

how do you calculate IKW(consumption per TR) in HVAC?..

Answer / sathish kumar

Ikw

Power input in kw for per ton of refrigeration KW/TR

FOR EXAMPLE 100TR CHILLER

FOR PRODUCING 100TR POWER CONSUMED 90 KW

IKW /TON = 100 / 90 = 0.9 i.e 0.9 KW /TON

to find IKW,COP,EER

If the power consumption is 1 kw /ton power consumption
system will provide cop of 3.5 and EER will be 12.

Is This Answer Correct ?    17 Yes 7 No

how do you calculate IKW(consumption per TR) in HVAC?..

Answer / virendra joshi

In general Practice you can consider 1 Tr = 1200 Watt = 1.2
kw

1 TR = 3.5 KW is next to impossible.

Is This Answer Correct ?    35 Yes 26 No

how do you calculate IKW(consumption per TR) in HVAC?..

Answer / sohal

to find out ikw
Amp.X Volts X Power-factor X 1.732/1000= kilowatts
then divided by machine tonnage = input kilowatt(IKW)

Is This Answer Correct ?    9 Yes 1 No

how do you calculate IKW(consumption per TR) in HVAC?..

Answer / sandip bharne

1Tr=80x907/24 ( ice requires 80kcal/hr to melt,907 is US
short ton)
=3023 Kcal

1kw= 860kcal/hr

1TR =3024/860
1TR =3.51KW

Is This Answer Correct ?    7 Yes 0 No

how do you calculate IKW(consumption per TR) in HVAC?..

Answer / carol

Be Carefull!!!!

TR and W are POWER UNITS
Btu is an ENERGY UNIT

As everyone knows from Basic Physics:

Energy = Power x time

The actual conversions are:

12.000 Btu/h = 1 TR
1 TR = 3517 W

Therefore,

12.000 Btu = 1 TR-h
12.000 Btu = 3517 kWh

Watchout!!!!!.....

Is This Answer Correct ?    8 Yes 2 No

how do you calculate IKW(consumption per TR) in HVAC?..

Answer / shri narayan gond

I know that 1 kw = 3413 B.T.U. and 1T.R.=12000 B.T.U. ,1T.R.=12000/3413.=3•5Kw.
Santiry fugle chiller I.K.W.=lode k.w./T.r.
For ex. My chiller capacity is 760 tr. And lode
509 kw.
I.K.W. =509/760
Ikw =0•669

Is This Answer Correct ?    7 Yes 1 No

how do you calculate IKW(consumption per TR) in HVAC?..

Answer / pradip

1TR= 12000BTU = 3000KCAL = 3.516KW,It is a thermal Unit,
But IKW relate of Power Consuption of Kw/TR,
In market many HVAC systems area available,so every systems
has different IKW,
Example : for VRV system
1TR consume 0.95 to 1.2KW,
1TR=1.2KW,
so IKW =1.2

Is This Answer Correct ?    6 Yes 2 No

how do you calculate IKW(consumption per TR) in HVAC?..

Answer / ruka

1TR=3.5kW <-- Cooling Capacity
3.5kW/COP = Electricity Consumption; normally COP>= 3
COP = Coefficient of Performance

If COP = 3.5
then;

1TR = 1kW <--- Can be varie

Is This Answer Correct ?    5 Yes 1 No

how do you calculate IKW(consumption per TR) in HVAC?..

Answer / santosh chavan

we need saving power consumption in HVAC system. please share

Is This Answer Correct ?    5 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

how to combine two linear transformers...............

1 Answers  


magnetizer priciple

0 Answers  


I need to connect a synchronous generator to the grid using automatic synchronization and two circuit breakers (one for synchronization, one for end connection to the grid), how to determinate the required diameter of the cables?

0 Answers  


Hi, We facing one similar problem in our computers i.e we are newly constructed our design department after that shifted our computers but our computer desktop screen is vibrating. we are conducted our electrical maintainance person he told that is UPS problem, then we changed the UPS also again we are facing that problem in that room only. then we put lcd monitors that problem is solved. But in other monitors why the computer desktop screen is vibrating please give a suggestion to me. Regards, Raju.N.G

10 Answers  


wat is the difference between rotor 1st stage fault and 2nd stage fault?

3 Answers  






How we can calculate what type of supply we need for an example sometimes we take 11 KV and sometime 33KV from EB ?

4 Answers  


List examples of current sources?

0 Answers  


all electricals questions

2 Answers  


What are the advantages and disadvantages of short-pitched winding?

0 Answers  


what will be the breaking capacity of MCCB of 1000kVA (6% Impedence) transformer? Voltage being 415V, Power Factor 0.8.

2 Answers   BPC,


can we use CBCT in neutral of solidly grounded transformer? in place of three phases we can pass only one phase which decreases the size of CBCT?

0 Answers   UPSC,


what is EBXl (electron beam cross linked ) cable ?

1 Answers   Polycab,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5084)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16631)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1094)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)