why we use to transmit the power in three phases intead of
single phase ?
Answers were Sorted based on User's Feedback
Answer / gunasekaran
power loss will more in single phase than 3 phase for
example we have to transmit 100A current for single phase
system .
2*Isqr*R= 2*10000*R=20000Rwatts
for 3 phase system 3*Isqr*R=3*57.7sqr*R=10000R watts power
has dissipated so 3 phase system better than 1phase
| Is This Answer Correct ? | 6 Yes | 1 No |
1.in case a fault occurs in a line ,unlike single phase the
continuity of power supply will not be affected i.e the
other two lines of 3 phase will not get affected.
2.single phase loads can also be operated by connecting it
between line and neutral.
| Is This Answer Correct ? | 7 Yes | 5 No |
Answer / paul
I do not think the previous answer is correct. Three phase is more efficient (Power In v Power Out) in respect to AC motors, and is also more cost economical in regards to power transmission as less copper is required for the same delivered power (given the 3 phase line voltage is taken as being he same as the equivalent single phase voltage therefore allowing the use of cable with the same voltage rating), however..
The transmission power loss (and therefor transmission efficiency) in a three phase systems is the same as in a single phase system (again, assuming same total load power and line voltage).
The previous response has omitted the fact that, even though there is no neutral wire the return current in a three phase system will be subject to I^2*R losses in the associated conductors. Taking R as the loop resistance (supply and return), a single phase system power loss can be calculated as I^2*R. For a balanced three phase system, the single phase equivalent losses will be ((I/root3)^2)*R. Therefore total losses = 3*((I/root3)^2)*R = I^2*R.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / bala
l.power generation is 3 phase. so power transmission also
in 3 phase.
2.Quantity of power transmission also consider in case of 3
phase we can transmit more power than conpare to single
phase.
| Is This Answer Correct ? | 4 Yes | 7 No |
What is the difference between power cable and signal cable (only Observation Difference)?
what is meant by impedance testing of transformer and why it is used
How do performance buccholz relay testing in power transformer
Differentiate between power relay and reverse power relay?
What will happen if the rotor circuit of a slipring I.M. is kept open & electric supply is given to its stator winding.
what is the use of excitation transformer in LAVT PANEL?
what is the power factor
13 Answers Heidelberge Cement,
What the purpose of transient fault recoredr in substation
block diagram of 2 ups system connected in parallel mode?
what is the relationship between current&voltage in practical purpose ?
300m long and 30kw inductive loade 3phase supply how many size cable required
in a plug point why the hole size at the top is large?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)