why we use to transmit the power in three phases intead of
single phase ?
Answers were Sorted based on User's Feedback
Answer / gunasekaran
power loss will more in single phase than 3 phase for
example we have to transmit 100A current for single phase
system .
2*Isqr*R= 2*10000*R=20000Rwatts
for 3 phase system 3*Isqr*R=3*57.7sqr*R=10000R watts power
has dissipated so 3 phase system better than 1phase
Is This Answer Correct ? | 6 Yes | 1 No |
1.in case a fault occurs in a line ,unlike single phase the
continuity of power supply will not be affected i.e the
other two lines of 3 phase will not get affected.
2.single phase loads can also be operated by connecting it
between line and neutral.
Is This Answer Correct ? | 7 Yes | 5 No |
Answer / paul
I do not think the previous answer is correct. Three phase is more efficient (Power In v Power Out) in respect to AC motors, and is also more cost economical in regards to power transmission as less copper is required for the same delivered power (given the 3 phase line voltage is taken as being he same as the equivalent single phase voltage therefore allowing the use of cable with the same voltage rating), however..
The transmission power loss (and therefor transmission efficiency) in a three phase systems is the same as in a single phase system (again, assuming same total load power and line voltage).
The previous response has omitted the fact that, even though there is no neutral wire the return current in a three phase system will be subject to I^2*R losses in the associated conductors. Taking R as the loop resistance (supply and return), a single phase system power loss can be calculated as I^2*R. For a balanced three phase system, the single phase equivalent losses will be ((I/root3)^2)*R. Therefore total losses = 3*((I/root3)^2)*R = I^2*R.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / bala
l.power generation is 3 phase. so power transmission also
in 3 phase.
2.Quantity of power transmission also consider in case of 3
phase we can transmit more power than conpare to single
phase.
Is This Answer Correct ? | 4 Yes | 7 No |
how to find number of run cable laying[LT side] for transformer & alternator secondary side? [above condition for getting output power transformer to main panel side] give the example.
in pf lagging means current decrease by increasing voltage is correct or not ? reason ?
what will be the energy loss =? Voltage drop = ? Conductor resistance at 20 degree C = ? Temprature convertion Factor at 50 degree c = ? on ACSR DOG Condutor at following data. distance = 4.8 kM Load = 2980 kWh Size of Conductor = 6/ 0.186 Volt = 11 kV.
1 Answers Pakistan Atomic Energy Commission PAEC,
Sir Power transformer :- (in generating station) Alternator terminals side - Delta HT transmission line side - Star Why?
Why CT's shall not be kept open?
5 Answers ABC, Qatar Gas, TIPL,
what is the different between bus section and bus coupler
corona happens more in summer or winter?
In case of any eventuality, who is your next of kin?
2 Answers Edison, Foster Wheeler, GE, GE Energy, HP, Infosys, Koch Industries, Roper Industries, Siemens,
Why electrical power generation and transmission done in 3 phase system not more than 3 phase ?
What is the function of restraining coil in differential relay? as well as restraining current?
If UG power cable both ends are to be earthed or what? If not why?
when a machine act as genartor and as motor?