Answer / kamal ghasemi

When the line isolator is open and the voltage from cvt to
distance relay is absent and the bus isolator and breaker
are closed; if a fault occurs between the line isolator and
the ct a feature in dist. relay called stub protection
which is an instatanious none diretional oc relay sends
trip command to breaker.This is usually in test and service
conditions.

Is This Answer Correct ?    174 Yes 14 No

what is STUB protection in tranmission system and switch yard area?..

Answer / vishvajeet sharma

above written is right, one more thing stub protection will
be active only when it get the status of line isolator as
open.

Is This Answer Correct ?    72 Yes 9 No

what is STUB protection in tranmission system and switch yard area?..

Answer / furqan ahmad

stub protection is used to protect the part of one and half breaker scheme which is not protected by distance protection.
it is active only when line isolator is open, and there is no voltage from cvt for distance protection.it is an over current relay which sense the fault and trip bus breaker under such condition.

Is This Answer Correct ?    41 Yes 8 No

what is STUB protection in tranmission system and switch yard area?..

Answer / abdelrahman hussein

The stub bus element protects for faults between two breakers in a breaker-and-a-half or ring bus configuration when the
line disconnect switch is open. At the same time, if the line is still energized through the remote terminal(s), differential
protection is still required (the line can still need to be energized because there is a tapped load on a two-terminal line or
because the line is a three-terminal line with two of the terminals still connected). Correct operation for this condition is
achieved by the local relay sending zero current values to the remote end(s) so that a local bus fault does not result in
tripping the line. At the local end, the differential element is disabled and stub bus protection is provided by a user-selected
overcurrent element. If there is a line fault, the remote end(s) trips on differential but local differential function and the DTT
signal (if enabled) to the local end are blocked by the stub bus logic, allowing the local breakers to remain closed.

Is This Answer Correct ?    7 Yes 0 No

what is STUB protection in tranmission system and switch yard area?..

Answer / m.balaji

When the line isolator is in open condition in between ct &
line isolator protection is called stub protection.when the
line isolator open condition then only stub protection enable,
if it's line isolator closed protection it will not check
distance protection relay operation required voltage so that
without voltage it will not operate ,so that time going to
fourth stage of over current it will happen only at the time
of ct saturation (or) surge.

Is This Answer Correct ?    7 Yes 6 No

what is STUB protection in tranmission system and switch yard area?..

Answer / anil

The above said is dead zone protection not stub

Is This Answer Correct ?    2 Yes 1 No

what is STUB protection in tranmission system and switch yard area?..

Answer / m. usman ali

During a line open condition with the station breakers
closed, the bus between the station breakers and line
disconnect for ring bus and breaker and a half/third
configurations may not be protected. The line protection
system shall be capable of protecting the open stub through
the use of overcurrent protection. This protection shall
also function correctly for the case where the potential
transformers for the line protection are located on the
line side of line disconnect whether or not the line is
energized from the remote end.

Is This Answer Correct ?    4 Yes 6 No

what is STUB protection in tranmission system and switch yard area?..

Answer / saadiq

STUB PROTECTION IS USED AGAIST THE POSSIBLE FOR THE
UNPROTECTED ISOLATOR WITH EARTH SWITCH ( WHICH IS BEYOUND
CT)

Is This Answer Correct ?    18 Yes 25 No

what is STUB protection in tranmission system and switch yard area?..

Answer / engr.irfan sajid

In one and half circuit breaker scheme,when the bus bar side
CB opened ,the area between central/tie breaker and bus bar
side breaker is called stub area where only voltages are
available but no current flowing i.e tee branch.When a fault
occurs in this area the over current element of bus bar
protection activated which after time delay i.e 100ms, trip
the central breaker and also send direct transfer trip
signal to remote end feeder to isolate the faulty area.

Is This Answer Correct ?    6 Yes 13 No

Post New Answer

More Electrical Engineering Interview Questions

what is the function of short circuit maintenance ct and droop ct.

1 Answers   L&T,


What is the power factor you maintain at ur organization?

43 Answers   Cummins, Exide, Johnson and Johnson, KTC, Microsoft, Powergear, Secure Meters, Suncity Strips, Wheels India,


working principle of induction motor is similar to transformer. but what makes it to rotate? then why the transformer doesnt?

4 Answers  


What is the Difference Between choke & ballast

3 Answers   ABB, ICS Integrated Computer Solutions,


why ct secondary side shortlink provided? its open what will happen?while running ?

2 Answers   Essar,






plz tell me in my que,how to connect thw electrical wirening in house?

1 Answers  


What are the types of transformers according to the arrangement of iron cores?

0 Answers  


What is meant by the KA-rating of a circuit breaker? In this regard, discuss the stresses experienced by the circuit breakers

3 Answers  


What is a variable speed motor?

3 Answers  


We have a 12MW power plant & we inject 5-6MW power to Orissa GRID. For this we have a 33KV/11KV switch yard having 12.5MVA power transformer. Some times we draw power during emergency. It is observed that during Export or Import for load less than 500Kw the power factor is decreasing to 0.3 . This is happening only during export or import. During island condition TG power factor OK.Our capacitor bank is provided with our Power plant auxilliary load. Please suggest how I can we improve our power factor during low load (GRID).

3 Answers  


A 3 phase transformer's (Y-Y) Y and B phase is (Y and B connection not broken) broken from neutral and R and Nutral connection is ok, what will be the relay tripping and why

0 Answers  


What is cathode ray oscilloscope (cro)?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5084)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16631)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1094)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)