Why SF6,VCB,Oil Ckt Breakers are use in HT Side need brief
information ?
Answers were Sorted based on User's Feedback
Answer / md ahmeduddin farooqi
the maintenance cost, I believe that SF6 Breaker is still
cheaper than the Vacuum Circuit Breaker because Vacuum
Circuit Breaker does have any limited operation life. For
Vacuum Circuit Breaker, there is limited operation life. You
need to change all the Vacuum breaker poles if the operation
life is up.
I don't know what is your intake voltage in this case, for
us, we use SF6 Circuit breakers for all the 11KV, 33kv.
Current interruption in a high-voltage circuit-breaker is
obtained by separating two contacts in a medium, such as
SF6, having excellent dielectric and arc quenching
properties. After contact separation, current is carried
through an arc and is interrupted when this arc is cooled by
a gas blast of sufficient intensity.
Gas blast applied on the arc must be able to cool it rapidly
so that gas temperature between the contacts is reduced from
20,000 K to less than 2000 K in a few hundred microseconds,
so that it is able to withstand the transient recovery
voltage that is applied across the contacts after current
interruption. Sulphur hexafluoride is generally used in
present high-voltage circuit-breakers (of rated voltage
higher than 52 kV).
Is This Answer Correct ? | 18 Yes | 6 No |
Answer / veeresh m y
SF6 Used in HT Side is Only the Main Reason is TO Avoide
the Heavy Sparks In the High Voltage Side.
Is This Answer Correct ? | 13 Yes | 4 No |
Answer / ashoke
Because the air circuit beakers are unable to quench the arc
immediately due to High voltage and current.So a more
efficient arc quenching medium is require like
oil,vacuum,SF6 in side.The HT contains higher voltage level
and the fault current is also higher so a brief description
is needed for choosing the appropriate CB.
Is This Answer Correct ? | 7 Yes | 4 No |
Answer / arvind kumar sinha
we use VCB and sf6 due to its high dielectric strenghth.
Is This Answer Correct ? | 3 Yes | 5 No |
If you have an earth with pilecap then your resistance is really low. why and how?
explain safety measures in alternator?
why transformer rating in KVA or MVA instead of KW n MW??
100V supply is appllied between 500K Resistance bulb. for 1 kwh energy, how long time the bulb will glow? explain the calculating method.
When testing an earthing connection, we use a 60 or 100 candle bulb with a phase connected direct from supply and the other wire to the new earthing provided.If the bulb glows then the earth is ok.Else earth connection is not Ok. So, why dont we can use all the home appliances taking a single wire from the phase and the return connection to Earth instead of return connection to neutral?
How Can You Relate Power Engineering With Electrical Engineering?
my bachelors was done with EEE now i got admit in NU with CS as course. how to answer this qns 1) why u choose cs? 2) why u changed from eee to cs
Why is remote backup preferred to local backup?
TNC switch is also available in 1NO+1NC. What does it mean ?
define regulation
60 watt bulb and 1500watt iron which device has more resistance & why