Hi frnds :)
plz tell me that i have 100 KVA 3 phase generator so by
thumb rule 100*1.4 = 144 amps
and generaly we can operate at 80% load...so it will 144*0.8
=112 amps....
so now i m confused about single phase load.....if we use
that generator only for single phase the that 112 amps is
total single phase load or i can give 112 amps at red 112
amps at yellow and 112 amps at blue....
i mean that total single phase load that 100 KVA generator
will take is 112+112+112=336 amp ??
Answers were Sorted based on User's Feedback
Answer / ramesh
No You cannot take 112 amps in each phase. you can take 112 amps in the sumation of r,y and b phase. (ie)total load current = Rph + Yph +Bph current.
| Is This Answer Correct ? | 4 Yes | 1 No |
Current in each phase 112 A ,ph voltage say 230 V. Then
apparent power in each phase is about 26 KVA .Sum = 78 KVA
which is almost the permissible load on the gen. If you add
phase currents ,the resultant is zero as they are vector
quantities . You can have a load of 112A in each phase .
| Is This Answer Correct ? | 0 Yes | 3 No |
Application Comparison between 22KV (UE)and 33KV (E) system. Are we allowed to use 33KV (E) cable in lieu of 22KV (UE) cable. What are the technical disadvantages.
How much of the total hydro power potential has been exploited so far in india?
We are installing a 1.6 MVA transformer at our crusher plant and the feeder of HPSEBL is 2 km away at substaion . and a VCB is installed in the substaion which is 2 km away from transformer so we need another VCB near the transformer.
What will happen if the oil level in the buchholz realy of a transformer gets down?
Can you explain about TEE protection scheme?
Can 4pole (3 phase+neautral )RCCB proper functioning in only 3 phase load (no neautral, no Earth) ?
why we have and use 3 phase not 2 or 4 or other in power system?
why we are useing capciter in EB meter?
why generator and t/f ratings given in kva & motor rating is in KW?
Can we use a window type neutral CT instead of a bar type neutral CT. We have an issue with a neutral bar type CT of 800/1 ratio with a Circuit breaker NS800L shneider type, and we want to change it with a window type. Pls advise. Thanks
how to select short circuit current while selecting a MCCB? how to calculate current for a given KVA and KW load?
2 Answers GE, PnU Engineering,
Does magnetomonopoles exists? one maxwell equation strongly suggests no, but how about their existance in plasma?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)