what is STUB protection in tranmission system and switch
yard area?
Answer Posted / m. usman ali
During a line open condition with the station breakers
closed, the bus between the station breakers and line
disconnect for ring bus and breaker and a half/third
configurations may not be protected. The line protection
system shall be capable of protecting the open stub through
the use of overcurrent protection. This protection shall
also function correctly for the case where the potential
transformers for the line protection are located on the
line side of line disconnect whether or not the line is
energized from the remote end.
| Is This Answer Correct ? | 4 Yes | 6 No |
Post New Answer View All Answers
What is dynamo?How it works and what is the function of dynamo in a DG.
How Self works in DG set
If I bring a basic electric meter from the States and hook it up in Costa Rica in a development that has only one transformer for the 50 homes, will it still be accurate regarding the usage of kilowatt hours?
which capacity of RCCB used for five thousand watt electricity load?
How can calculate the rating of a alternator for a given specific load with formula
What is conventional thermal current (Ith)
How to calculate the fuel consumption for 600kva DG genset which connecting with 25%load?
how to measure dc earth leakage current?
Q.1:What protection will be used on HT and LT side of 33/0.4 KV, MVA transformer. Indicate capacities of protective device to be used. Q.2:Which types of back-up protections are used in the power transformers? What do you understand by the term over travel in the relay? Q.3:How star and delta connected winding transformer are provided from earth fault
For overhead protection we use which transformer?
hi, could someone help me to find a control design for syncronising panel .
which phase is preferred for connecting 1 phase vt used for synchronizing OHL? WHY?
How you will determine the volume of oil in a particular Distribution transformer.
what is the acceptable limit value for Desolve Gas Analysis/
what is the effect of earth on capacitance in 3-phase and 1- phase transmission line?