Answer Posted / m. usman ali

During a line open condition with the station breakers
closed, the bus between the station breakers and line
disconnect for ring bus and breaker and a half/third
configurations may not be protected. The line protection
system shall be capable of protecting the open stub through
the use of overcurrent protection. This protection shall
also function correctly for the case where the potential
transformers for the line protection are located on the
line side of line disconnect whether or not the line is
energized from the remote end.

Is This Answer Correct ?    4 Yes 6 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

how the works electronic energy meter?

1654


What are all present producing cost of Per KWH of various Fuel?

2112


what is invertor supply and raw powersupply

1521


Has someone here done a sizing for a generator (3 phase), its for a pumping station. If you have an example for standby/duty and both running (I) star delta (ii) Soft Starter.

1611


What does the letter CTNM in negative phase sequence relay means?

1215






what is the difference between rectifier and converter and commudator?

1467


How many types of electric motors are there?

647


What is the need of earthing transformer for delta side of a transformer. (Think of a line section between a star/delta transformer at a grid substation and delta/star transformer at a village. An earthing transformer is there at the delta side of the star/delta transformer at grid substation). As there are no ground reference there will not be fault current if a one phase is grounded. Further L-L phase will be sensed by the primary side of star/delta transformer as a L-G fault. So why an earthing transformer is required at delta side

966


How to select cable the size, what is the parameters use and what is the formulas use for this cable size calculation?

1406


Load transfer in 11kv double busbar switchgear - operation.

1492


Explain about Leakage Test.

1443


what is ps impedance test

1651


Why lose 1 phase voltage in 33kv to 415v stepdown transformer

1307


WHAT IS THE WORKING PRINCIPLE OF A GENERATER.how is a GTG (Gas TURBANE Generater) working.plz explane

2056


what about SAP/MRP regarding manufacturing of electric motors and all drives?

1568