what is STUB protection in tranmission system and switch
yard area?
Answer Posted / m. usman ali
During a line open condition with the station breakers
closed, the bus between the station breakers and line
disconnect for ring bus and breaker and a half/third
configurations may not be protected. The line protection
system shall be capable of protecting the open stub through
the use of overcurrent protection. This protection shall
also function correctly for the case where the potential
transformers for the line protection are located on the
line side of line disconnect whether or not the line is
energized from the remote end.
Is This Answer Correct ? | 4 Yes | 6 No |
Post New Answer View All Answers
how the works electronic energy meter?
What are all present producing cost of Per KWH of various Fuel?
what is invertor supply and raw powersupply
Has someone here done a sizing for a generator (3 phase), its for a pumping station. If you have an example for standby/duty and both running (I) star delta (ii) Soft Starter.
What does the letter CTNM in negative phase sequence relay means?
what is the difference between rectifier and converter and commudator?
How many types of electric motors are there?
What is the need of earthing transformer for delta side of a transformer. (Think of a line section between a star/delta transformer at a grid substation and delta/star transformer at a village. An earthing transformer is there at the delta side of the star/delta transformer at grid substation). As there are no ground reference there will not be fault current if a one phase is grounded. Further L-L phase will be sensed by the primary side of star/delta transformer as a L-G fault. So why an earthing transformer is required at delta side
How to select cable the size, what is the parameters use and what is the formulas use for this cable size calculation?
Load transfer in 11kv double busbar switchgear - operation.
Explain about Leakage Test.
what is ps impedance test
Why lose 1 phase voltage in 33kv to 415v stepdown transformer
WHAT IS THE WORKING PRINCIPLE OF A GENERATER.how is a GTG (Gas TURBANE Generater) working.plz explane
what about SAP/MRP regarding manufacturing of electric motors and all drives?