how to calculate circuit breaker capacity
Answers were Sorted based on User's Feedback
Answer / hari
If u have the fault mva and the voltage level at which the
CB is to be installed then :
Normal current would be the continuous current flowing in
the line ( u can take the next higher value from standard
values to take care of over current)
Breaking capacity would be tha fault MVA.
Rated symmetrical breaking current in kA would be Fault
MVA*1000/(1.732x Voltage in kV)
Rated making ct would be peak value of symmetrical breaking
current i.e 2.55 times breaking current
Short time rating would be rated symm breaking ct for 3 secs
| Is This Answer Correct ? | 95 Yes | 17 No |
Answer / ravi kumar singh
Breaking capacity will be always iN MVA= 1.732*Voltage in KV * cerrent in KA
making capacity = 2.55 * symmetrical breaking capacity
note:-( 1.41*1.8=2.55)
full load current= 1.8 * KVA
ravi kumar singh
| Is This Answer Correct ? | 51 Yes | 10 No |
Answer / nighot jagdish
Rated symmetrical breaking current in kA would be Fault
MVA*1000/(1.732x Voltage in kV
| Is This Answer Correct ? | 50 Yes | 19 No |
Answer / karthik
BREAKING CAPACITY OF CIRCUIT BREAKER
=SQRT(3) x V x I x 10-6
V is supply voltage
I is circuit breaker capacity
answer appears in MVA.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / usama badran ali
el salamo aleekom
to calculate circuit breaker breaker capacity...there are
four steps :
1-indicate all actual nominal voltages and MVA of your
system
2-indicate the location of circuit breaker.
3-calculate the actual impedance between the known supply
to the point of fault at which near to circuit breaker.
4-then calculate:
a- short circuit current =
voltage of supply/((3^0.5)actual impedance)
b-MVA short citcuit=
(3^0.5)*voltage of supply*short circuit current
c c-breaking capacity=
MVA short citcuit*assymetry factor.
or
short circuit current*assymetry factor
notes:
Assymetry factor:1.5~1.6 for midium voltage
1.25 for low voltage
MVAshort circuit= fault level
breaking capacity: it is the value of peak current where
the circuit breaker is breaking.
| Is This Answer Correct ? | 8 Yes | 11 No |
we can consider circuit breaker capacity for particular
feeder depend upon the 1.2 times of full load current for
receiving end equipments
| Is This Answer Correct ? | 4 Yes | 12 No |
What should be value of Circuit breaker operating time and tripping time?
Why is it that polarization index type test is required for MV and HV motors and not for LV motors?
3 Answers La-Gajjar Machineries, Qatar Airlines,
how bucchos relay works in a transformer
i want to measure voltage difference between neutral and earth so i just simply use voltmeter. my question is that may i use this measure continuosly.or there are some electricity board restrication on that? or it creat some problem on my measuring device..?
what do you mean by PF correction. A motor is rated at 15 kw,415 volts, 0.7 pf and eff of 0.92. The powerfactor is improved to 0.98 by adding capacitors at the bus. calculate the current drawn by motor under full load condition before and after pf correction
What is phase in electrical engineering?
What is PTZ Camera???
3 Answers Cherrytec, CSC, Honeywell, Zicom,
What is Diff. btw Cat-5 & Cat-6 Network Cables???
what mean ohm
what is means of ALF,kPV(min),lexc(max)at Vk,Rct@75 degree centrigate ohm in current transformer name plate?
is there interlocking between duty and standby chilled water pumps?
Why neutral shows voltage with earth ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)