how to calculate circuit breaker capacity
Answers were Sorted based on User's Feedback
Answer / hari
If u have the fault mva and the voltage level at which the
CB is to be installed then :
Normal current would be the continuous current flowing in
the line ( u can take the next higher value from standard
values to take care of over current)
Breaking capacity would be tha fault MVA.
Rated symmetrical breaking current in kA would be Fault
MVA*1000/(1.732x Voltage in kV)
Rated making ct would be peak value of symmetrical breaking
current i.e 2.55 times breaking current
Short time rating would be rated symm breaking ct for 3 secs
| Is This Answer Correct ? | 95 Yes | 17 No |
Answer / ravi kumar singh
Breaking capacity will be always iN MVA= 1.732*Voltage in KV * cerrent in KA
making capacity = 2.55 * symmetrical breaking capacity
note:-( 1.41*1.8=2.55)
full load current= 1.8 * KVA
ravi kumar singh
| Is This Answer Correct ? | 51 Yes | 10 No |
Answer / nighot jagdish
Rated symmetrical breaking current in kA would be Fault
MVA*1000/(1.732x Voltage in kV
| Is This Answer Correct ? | 50 Yes | 19 No |
Answer / karthik
BREAKING CAPACITY OF CIRCUIT BREAKER
=SQRT(3) x V x I x 10-6
V is supply voltage
I is circuit breaker capacity
answer appears in MVA.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / usama badran ali
el salamo aleekom
to calculate circuit breaker breaker capacity...there are
four steps :
1-indicate all actual nominal voltages and MVA of your
system
2-indicate the location of circuit breaker.
3-calculate the actual impedance between the known supply
to the point of fault at which near to circuit breaker.
4-then calculate:
a- short circuit current =
voltage of supply/((3^0.5)actual impedance)
b-MVA short citcuit=
(3^0.5)*voltage of supply*short circuit current
c c-breaking capacity=
MVA short citcuit*assymetry factor.
or
short circuit current*assymetry factor
notes:
Assymetry factor:1.5~1.6 for midium voltage
1.25 for low voltage
MVAshort circuit= fault level
breaking capacity: it is the value of peak current where
the circuit breaker is breaking.
| Is This Answer Correct ? | 8 Yes | 11 No |
we can consider circuit breaker capacity for particular
feeder depend upon the 1.2 times of full load current for
receiving end equipments
| Is This Answer Correct ? | 4 Yes | 12 No |
what the reson to use phase shift( angle) like (dyn11,Dd5 or Dy0)are usedin power and transsmison line
There are two nos of 33Kv/11Kv 5MVA transformers conecting through HT cable from substation having metering at substation itself.One transformer used at a time another remains stand by.Further 11 nos of 11Kv/440V transformers are attached on it and each transformer is having its own Power factor correction panel.Now one 33/11Kv transformer at no load condition/Stand by condition is having power factor in leading side upto 0.21 and while when another tranformer at same situation have power factor in lagging 0.42. Now one thing is clear that transformer one is having 1.5 Km long 33kv cable due to that PF goes in leading side and another is having only 250 mtr length remains him lagging. Now i want to know that how i can maintain the Power factor at no load/ stand by position though both are behaving in seperate manner.
how can we phase identification in a distribution line,how we recognise that which phase is coming for a house hold connection.help me............
If o/p power is doubled by how much does the sound increase
Is it posible to instal one more SMDB from the existing SMDB and is it practical.
How to select the releases for MCCB ?
how is efficincy of the transformer is predermined
why ahould you show client/engineer activities clearly on the project plan
how to calculate AH of a battery?
What is the diffrence between PS & metering CT (5p20,0.5 etc.)? Why in PS class CT only Vk is given ? Is PS class CT is more accurate than metering CT?
What is the formula to calculate the rating of a thermal over load relay
1. What is maximum permissible distance between smoke detectors ? 2. How do we decide number of smoke detectors required in a large office, warehouse, hall etc ? 3. What should be maximum height of smoke detectors ? 4. Where do we use heat detector, optical smoke detector, temperature sensitive detector ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)