Why is it that polarization index type test is required for
MV and HV motors and not for LV motors?
Answers were Sorted based on User's Feedback
The polarisation index is used to check the insulation of
MV and HV motors because it is more accurate. Also it
allows a lower voltage than the working voltage of the
motor to be used. In LV motors the megger test is usually
twice the working voltage. If this was used on an 11kv
motor the megger would need to be 22kv.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / cr
As we r letting high current pass through the winding using ht megger,there by improving I.R because the heat produced and the ir ratio for 10 to 1 minute should be around 2.otherwise the insulation can be said to be contaminated with foreign meterial , this check is priority for ht motors
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / prashant
because the moror windig is balance or not and winding of the motor is open or not
| Is This Answer Correct ? | 0 Yes | 7 No |
how to test a motor from megger
How to calculate the KA rating for a circuit breaker if we know the KVA rating of the generator feeding it?
A 6.6 KV/ 440V Xformer. what are the imporatant parts & equipment required for it's protection panel.
In radial network the source is fed from 1 end both ends at central
What is the name of oil which is used in transformer?
is any body explain me why return current in three phase power system is less then in a red, yellow, blue phases??? as we know Ir+Iy+Ib=In then why nutral wire has less then phase current????
What will happen when we will connect lamp in between phase and earth.
What is the different between conventional MCC and intelligent MCC? Common controller or controller for each bucket
what will happen if we use cylindrical conductor instead of flat cu conductor in transformer
what is meant by generator differencial protection?
What will happen if i connect the delta winding motor to star input.
WHAT IS AIR GAP VALUE IN MM FOR A 11KV BUSHING OF 11KV/440V DISTRIBUTION TRANSFORMER. AND AIR GAP VALUE OF 25 KV BUSHING OF AT TRANSFORMER OF 25 KV TRACTION. WHAT IS THE CALCULATION FOR THE AIR GAP PERMITTED FOR BUSHINGS AT DIFFERENT VOLTAGES.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)