how bucchos relay works in a transformer
Answers were Sorted based on User's Feedback
It is a gas actuated relay.It has two floats.
one is top float(bucholz alarm) which is operated when
oil level in transformer decreases and for a minor fault
which is developing.The gas is collected at the top of
bucholz relay, thus displacing the oil in the top and thus
causes the float to fall down and make the NO contact.
The other is bottom float(bucholz trip) which is
operated for a severe fault which causes oil inrush towards
the bottom of bucholz relay and thus causes the float to
make the NO contact thus isolating the supply to the
transformer.Sometimes buchols relay will operate for a
feeder through fault which causes jerk in the transformer
causing oil inrush.
cheers
gova
| Is This Answer Correct ? | 17 Yes | 1 No |
Answer / minal
When there is a fault in a transformer gas bubbles are
formed in an oil filled transformer, the bucholz relay
operates & it gets trip .Thus it protects the tranformer
from any fault.
| Is This Answer Correct ? | 16 Yes | 4 No |
Answer / gajanan
The Buchholz relay is installed at the middle of the
connection pipe between the Transformer tank and the
conservator.
for the fault in transformer it actuates the alarm or the
Transformer is disconnected from the circuit for severe
fault
| Is This Answer Correct ? | 14 Yes | 4 No |
Answer / vinayak khorate
In oil filled transformer the bucchos relay is mounted in
between connection pipe of Transformer tank and the
conservator.
When fault occurred(slow occurring faults) the oil near by
winding gets heated and decomposed due to which gas bubbles
are release. This bubbles get stuck in the Oil chamber of
reply and hence send the tripping signal. When the fault is
heavy large number of gas bubbles are released, when they
pass over the bucchos reply the tripping mechanism in between
gets triggered and Transformer is disconnected from the
circuit for severe
fault
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / gunasekaran
during the incifient fault 75%H2 gas will be form in the
transformer is gas accumulate at buchholz relay first it
will give alarm then trip
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / anil kumar
whenever it is incipient fault in transformer, the gaseous formation take place which moves up wards from bucz relay, and replaced the oil in upper tub and press the tub , so due to mercury switch, ckt will complete & alarm will appear , if further severe fault , the oil pr. increases in tank and will go in conseverator tank through buz relay which makes press the bottom tub forcibly and trip the ckt .
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mukesh vaghela
Buchholze relay is gas operating relay when internal fault occurs transformer in transformer like wdg installation damage then oil heat above level and boobles done and go up and its pressure operate buchholz relay. It is only relay which operate before fault occurs in system.
| Is This Answer Correct ? | 0 Yes | 0 No |
In a transformer ,when voltage decreases current increases. but this is a violation of oms law.why?
hello every one, what is the difference between the Kvar and farads, Rating on Power capacitor is for eg: x kvar, and normal capacitor is eg: x farads. what is the relation between these two?
what is maximum or Threshold value of current 7 voltage that a common man can withstand
Hello sir. if u have electical engineering exam paper then plz mail me at bhumika_1187@yahoo.co.in. i m appearing exam for HPCL.
SIR, GIVE ME OPGW SAG CALCULATION FORMULA I AM DAE ELECTRICAL. THANKS
Can anybody please refer the best and simple book for about Protection relays and in detail of all its protection ?
how would you come to know if a transformer is double wound or auto? note that there is no tag. you are given only a multimeter.
What size cable (based on voltage drop) is required to supply a 40 A three phase boiler if the wiring system is 75V single insulated cables installed in non-metallic rigid conduit 56m from the main switchboard? Voltage drop in the consumer's mains is 8V.
kVA rating of open delta connected transformer is _____% kVA rating of delta/delta connection A 50 B 70.7 C 57.7 D 75.7
What Factors should we consider while synchronizing two DG Sets?
Can we generate 3 phase power from single phase connections?? If yes, how?
Send the control circuit digram of a star delta stater?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)