What is vector group? What is meant by DYN11?Why is it needed?
Answers were Sorted based on User's Feedback
Answer / avnish
above answers are correct but as u asked shraddha that will
hv lead or lv so i clear that capital D is for secondary and
small forthe primary and again 11 ....means that hv have the
30 degree leading phase diffrence..
| Is This Answer Correct ? | 2 Yes | 11 No |
Answer / ghost rider
Abobe two reply explained correctly "what is vector group".
The answer to the last question "why it is needed" is as
follows:-
By virtue of constrction & terminal connections of the
transformer, a difference between primary vector &
secondery vector occurs. We need to know the same for the
following reasons:-
1)Matching of vector group is required (to avoid
circulating current/ fault ), when 2 transformer need to be
operate parallal on a common bus/system.
2) to provide transformer differential protection correctly.
etc
| Is This Answer Correct ? | 8 Yes | 18 No |
Answer / strateia
The Dyn11 is interpreted as follows:
D-primary winding is delta connected (i.e the three primary
phase windings within the transformer)
y-the secondary winding is delta connected
11-is a multiplying factor for the phase displacement
between the primary and secondary voltages
i.e. for the Dyn11, phase displacement is
= 11*30degrees
= 330 degrees
| Is This Answer Correct ? | 10 Yes | 31 No |
what is the calculation involved to design the heater to heat 10KL of water in temperature control unit?
does any one know where we can purchase insulation oil for high voltage oil filled cables
what are the main problems that happen in an emergency light and how to fix them ?
A 100W electric lamp is supplied from a 115V, 60HZ source. The peak instantaneous power dissipated in the lamp filament is
how to select cable size?
in dc shunt motor if field winding is shorted then
how much Amp we can put in 1200kva generator?
WHAT HAPPEN IF GENERATOR TURBINE IF TRIP?
What are all present producing cost of Per KWH of various Fuel?
The rating of Transformer are 11KV, 22KV, 33KV instead of 10KV, 20KV & 30KV?
Why dc voltage used to excite alternator field in stead of ac?
I have 1 KW, 3ph. 440v, 50 hz, cos(phi) .75, efficiency 75%(star delta connection)Motor. How to calculate line current & Phase current (1) Star connection (2) delta Connection
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)