how to reduce earth to neutral voltage?
Answers were Sorted based on User's Feedback
Answer / shahed
earth to neutral voltage can be due to
1. improper or no earth
2. neutral currents flowing
By proper earthing techniques 1. can be solved.
For 2. the neutral current must be reduced . If possible
the rating of the neutral conductor can be increased therby
reducing IR drop. or an isolation transformer may be used
with it's secondary neutral connected to earth.
| Is This Answer Correct ? | 26 Yes | 1 No |
Answer / shailendra
By doing proper type of earthing with minimum ristance
value. earthing is to be done accordiing to the type and
moisture content of the soil of that particular area.
ASHLOK type earthing is most popular nowadays.
| Is This Answer Correct ? | 11 Yes | 7 No |
# 4 is the best & right answer by Shahed as I faced &
resolved this problem with this method only.
| Is This Answer Correct ? | 4 Yes | 1 No |
Dear Lalvijaybe,
Just reduce the earth resistance(proper earth connection
should be there).
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / vipin nain
1_ try to reduce earth resistance
2. Try to balance the loads in all phases.
3. Earthing should be prper nd connections should be brazed...no corrsion be there between joints....
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / gaurav patil
Earth pit resistance should be less than 5ohm hence your earthing found ok.or earth to neutral voltage less than 1V.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / raghav
To reduce NEV or earth resistance use Electrodes type earthing instead of pit earthing...
| Is This Answer Correct ? | 1 Yes | 5 No |
Answer / abdul rehman
Why induced static charges in transmission lines.
| Is This Answer Correct ? | 2 Yes | 11 No |
what are difference between indoor and out door substation
how to calculate the ct burden?
For polarity test on a 11/3.3kV 2.5MVA delta-star Unit Auxiliary transformer,415V 3-phase supply was applied at the HV. Connection between Aa was made with a 2.5mm cable. As soon as power was switched on the cable caught fire and burnt. This test was then abandoned. It is noteworthy to say that a similar cable was also used in a similar transformer for the same. The cable did not burn and test was successfully completed with good result. What is wrong? Please, help me out.
what are the checks of diesel gensets
How to design the no. of ceiling fans required in 5mtr X 10 mtr X 3 Mtr hight room?
can we connect both delta and star to the transformer secondary and for what reason?
what's the exact magnitude of current, flows through Neutral?
Approach of a cooling tower is the difference between temperatures of what factors?
I NEED RRB SYLABUS FOR JE ELECTRICAL ,PLEASE SEND TO MY E- MAIL ID joo28_eee@yahoo.co.in
What is the selection process of breakers. Can any one please give a formulation on same?
what is AB switch???
What will be the size of copper cable (each for 3 phase and 1 neutral) from Service connection Kit-Kat to Panel Board (i.e. to main switch) for a 6 pole 3-phase AC induction motor of 200 H.P. capacity? Amp-255 A, Frequency:- 1450 rpm.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)