how to reduce earth to neutral voltage?
Answers were Sorted based on User's Feedback
Answer / shahed
earth to neutral voltage can be due to
1. improper or no earth
2. neutral currents flowing
By proper earthing techniques 1. can be solved.
For 2. the neutral current must be reduced . If possible
the rating of the neutral conductor can be increased therby
reducing IR drop. or an isolation transformer may be used
with it's secondary neutral connected to earth.
| Is This Answer Correct ? | 26 Yes | 1 No |
Answer / shailendra
By doing proper type of earthing with minimum ristance
value. earthing is to be done accordiing to the type and
moisture content of the soil of that particular area.
ASHLOK type earthing is most popular nowadays.
| Is This Answer Correct ? | 11 Yes | 7 No |
# 4 is the best & right answer by Shahed as I faced &
resolved this problem with this method only.
| Is This Answer Correct ? | 4 Yes | 1 No |
Dear Lalvijaybe,
Just reduce the earth resistance(proper earth connection
should be there).
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / vipin nain
1_ try to reduce earth resistance
2. Try to balance the loads in all phases.
3. Earthing should be prper nd connections should be brazed...no corrsion be there between joints....
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / gaurav patil
Earth pit resistance should be less than 5ohm hence your earthing found ok.or earth to neutral voltage less than 1V.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / raghav
To reduce NEV or earth resistance use Electrodes type earthing instead of pit earthing...
| Is This Answer Correct ? | 1 Yes | 5 No |
Answer / abdul rehman
Why induced static charges in transmission lines.
| Is This Answer Correct ? | 2 Yes | 11 No |
how much up to LT Voltage range?
1.what is bus cuplour and main funtions. 2.what is main function of alternator. 3.how many types of dg oils.
I find that underground strip-armoiured,4core,LT PVC cables in an earthed power distribution sytem are occasionly found in charred condition-with no trace of it except ash. Is this because of no proper earth connection/continuity (giving rising to high armour resistance)in the joint enroute or because of insufficient capability (again due to high armour resistance)of cable-armour to carry fault current or due to neglected /unprotected overloading of the cable or due to high armour currents caused by power thefts where only phase(s) are unauthorisely tapped & at the point of poer consumption earth terminal is established by burring underground a not so good earthing rod (or using an underground water pipe for the purpose)
What is the actual meaning between the energy conservation and energy saving ?
how much allowable resistance that can be difference in motor all coils?
ratings of lightning arrester
advantages & disadvantages of Lagging and leading power factor .
What is the dc grounding system and what is diff between AC/DC grounding system?
What does the temperature (30 deg or 35 deg celcius) mark on conservator of transformer indicates?
WHY WE USE SIEMENS plC
How to calculate cable size in HT AND LT
what must be the mf for a meter with the following conditions. line ct ratio-100/1 line pt ratio- 220kv/110v meter pt ratio- 3X63.5V meter CT ratio- -/1 A
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)