Can CT Secondary left open circuited and why(reason)?
Answers were Sorted based on User's Feedback
Answer / jayakumar.k
CT Secondary should never let open condition. Since there
is no opposing flux in secondary circuit Primary flux will
develop enormously high that would cause bursting of CT and
also damage to the person who is working with it.( Remember
induction principle)
| Is This Answer Correct ? | 26 Yes | 0 No |
Answer / raul
absolutely NOT bcoz during normal operating conditions, the
primary and secondary current are equal and opposite to
each other.........so the mmf of both primary and secondary
are in direct opposition........but secondary current is a
bit lesser than d primary current and this difference is
utilised in magnetising the core.......but if the secondary
is left opened then there will be no demagnetising mmf left
and excessive flux will b generated in the core and due to
this enourmous amount of voltage will b produced in the
secondary which is very harmful for life and CT also. also
there will be a loss of accuracy in future due to residual
flux left in the core.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / muhammad nazim
A CT is basically a step-up transformer(from voltage point
of view).In the case of 400/1 A CT the primary turn is 1
(say the busbar)and the secondary turns is 400.How much
will be the primary voltage drop?? it will be in millivolts
for a busbar.So this millivolts multiplied by 400 will
cause just around a few volts (say 3 to 10V) for an open
secondary.But i have read that the secondary voltage will
reach a few kilovolts for a 400/1A CT at full load
conditions.My question is how it will reach a few kilovolts
and damage the CT on open secondary condition?As we have
seen above the max voltage wil be just in few volts.So
please someone
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / bharat sharma
Let us assume we have 600 V and 200 A on primary side of the
CT. Ct ratio is 200:1 In that case Secondary voltage would
be (600V x 200A)/1A = 120000 V. Would you like to leave
120000 V open circuit irrespective of current capacity of
secondary circuit?
| Is This Answer Correct ? | 8 Yes | 10 No |
Why power factor does not occur in DG set ?
In liquid rotor starter how PH valve should be maintained.
transformer 3 ph, 225 kva pri 480v, sec 208v. primary neutral connected to system, is secondary neutral to be grounded and how
What is the best thing to protect the motor from running over full current. CT or O/L or pressure transducer at the given pressure rating
Draw a 230kv two-bus bar system showing the following. 1.Two generators (150MW) each connected through one 15.75/230KV transformers 2. 1 outgoing lines 3. Two 230/130 KV transformers 4. BUS PT's 5. CT
What is the tension required for the 25000 CFM AHU belt
How does a VOLTAGE OPERATED DIFFERENTIAL RELAY work??
why dc is used in control circuit for mv & hv switchgear instead of ac
How we can find the regulation of transformer?
What is the height of DA, DAL, DB, DC & DDE tower?
what's the difference between ATS and AMF...??pls answer me in detail with its working principle and construction also..
What is the ratio of Booster transformer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)